tests

  1. Michael J

    Called to carry out live tests & certify

    I was called by the client to do final live test & issue EIC. Not so straight forward, not all cable chases have been plastered and a couple of areas where boarding has still to be completed. So annoying, anybody else come across this?
  2. A032701

    Tests to carry out prior to new CU

    hi i have been asked to quote for a job where the owner is doing an extension and wants me to do all new wiring in the new part however he wants to keep the existing wiring the same. he also wants to change over the cu to a new metal one (mk probably). What tests do people recommend i do on...
  3. M

    Mcb trips but tests clear

    Evening all Let’s see if anyone can solve this one. Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to...
  4. Marti

    Megger 1730 MFT. Not tripping on any RCD tests on known good circuit.

    G'd Evening Lads an' Lasses, I've got a Megger 1730 MFT; lovely bit of kit normally. Ex-demo - not had a hard life and was calibrated about eight weeks ago. I normally run it over a Cal-Card and a captive test RCD about once a month and this time it failed to trip the 30ma RCD on 1x, 5x and...
  5. Speedy

    Ola. I/R tests on lights

    When doing an Electrical Condition report what's the best way to do a live to neutral I/R test on a lighting circuit with LED's (600x600) or infact any lights in a large office?
  6. S

    Zdb before dead tests.

    Hi guys got my assesment in 3 weeks and want to get my testing spot on. Little confused whether to test Zdb on 2 way CU before dead tests?? Or do I jump straight into continuity? Thanks in advance.
  7. JK-Electrical

    Omission Of Tests On Inaccessible Kitchen Appliances

    Other than the testing of the usual kitchen appliances that landlords supply as part of the tenancy agreement, I very rarely do any other PA testing. I will be carrying-out an EICR later this week on a property that will soon be made available to let. All appliances bar one are enclosed within...
  8. W

    Neutral in zs tests ? If zs is

    Hello if zs is ze+ r1 + r2 Why when we test do we need the neutral whilst doing zs tests ?
  9. B

    DIY sockets tests when selling house

    Hi When we bought our house a few years ago (which the wife said we would never move out of) I added a number of sockets to the upstairs ring final using some lovely surface mounted trunking. I did quite a bit of research at the time to make sure it was safe and tested them all with a plug in...
  10. J

    Your thoughts required on industrial production qualifications and tests

    Hi Guys, I work for a international packaging company and we have had a death of an engineer in South Africa. He was changing a motor on a strapping machine and electrocuted himself, further details are not for coming yet. It has raised questions as follows and i was looking for your...
  11. weevilward

    Need some ideas - RCD tripping but everything tests fine....

    Hi all, Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test). I'm out of ideas here, can anyone help? This is what I've got: - TT installation (small domestic); - 30mA RCCB...
  12. D

    Experienced practically, learning theory

    Hello all, I've worked as a sparky for 3 years before now only deciding to do my tests, got level 3 unit 301 out of the way pretty quickly but dreading unit 302!!!! Any tips on what to revise formula wise? Am I going to need to know every formula?? Thanks, Dan
  13. J

    Tests for replacement consmer unit

    Could you tell me whether most of the tests carried out for a Domestic Electrical Installation Report would have to be repeated if a replacement consumer unit is subsequently fitted?
  14. T

    Anyone looking for a job in the midlands?

    Fixed Wire Tester Job in Bristol Jobsite - http://www.jobsite.co.uk/job/957722543?sctr=EN&utm_campaign=jbe-EN&src=email_minjbe&cid=JaJob-01-2017_vacancy&intcid=jajob-min&cid=&utm_source=jbe-min&utm_content=160317&utm_medium=email £3.64 per test, wonderful!
  15. the pict

    RCD issue, or is it?

    Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth...
  16. R

    >2000 ohms on loop test?

    Hi guys, Was wondering if anyone could shed any light on why I would be getting >2000 ohms on my loop tests, on every circuit? I got .26 on the incoming reading, went to do the test on the cooker circuit and >2000, thought I'd try back at the consumer on the incoming and >2000 again, I'm using...
  17. P

    Continuity Tests

    Is the continuity test for circuit protective conductors, the same test for ring and radial circuits or is there a different test for each type of circuit? Also what is the difference between testing for cpc continuity and testing for continuity for ring final circuit conductors?
  18. P

    Continuity Tests

    Is the continuity test for circuit protective conductors, the same test for ring and radial circuits or is there a different test for each type of circuit? Also what is the difference between testing for cpc continuity and testing for continuity for ring final circuit conductors?
  19. A

    Help 2395 written

    hello all, Failed my 2395 written exam and from wanted help understanding the following questions that came up State two reasons why it is important that the phase sequence is confirmed throughout the installation? State two methods to confirm phase sequence with an installation? The...
  20. A

    Help with 2395

    hello all, Failed my 2395 written exam and from wanted help understanding the following questions that came up State two reasons why it is important that the phase sequence is confirmed throughout the installation? State two methods to confirm phase sequence with an installation? The...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock