Hi all,
I've tested several radial circuits and only getting 0.00 ohms on the r+r2 test (zero'd leads)
2 of the radials only supplies one socket each and are approx. 3 metres in total length. (zs 0.25 and 0.21)
Another radial only supplies one socket and is appox. 5m in length. (zs 0.35)
The final radial supplies 2 sockets and approx. 7m in total length. (zs 0.53)
Are the readings due to the length of the run or could it be the batteries need changing on my Fluke Multifunction (even though no battery warning)
Thanks