Not working on this circuit but not sure what to do. The circuit appears to only supply an unused FCU which I'd like to disconnect in the CU but as it has nothing to do with the work I'm doing I cannot spend too much time investigating the full circuit.

I have isolated the MCB overnight and asked the customer to have a look round to see if anything else is fed from it with the intention of disconnecting it in the morning.

Is this the best way forward, can't bring myself to ignore it so would like to leave it as safe as possible without incurring hours of extra work I don't have the time to do.
 
Pete, Changing the MCB brings the circuit under my responsibility and I simply don't have the time to T&I it, I don't have a 6amp either.

Just checking that disconnecting it doesn't have any hidden consequences I haven't thought of.
 
Pete, Changing the MCB brings the circuit under my responsibility and I simply don't have the time to T&I it, I don't have a 6amp either.

Just checking that disconnecting it doesn't have any hidden consequences I haven't thought of.
What exactly were you there to do?
 
1.5 is the minimum for a power circuit, if the only thing connected is a fused spur then it can't pull no more than 13A. If the installation method permits adequate CCC and the CSA is adeqate for fault current/thermal constraints under fault conditions then technically there is nothing wrong with it.
 
1.5 is the minimum for a power circuit, if the only thing connected is a fused spur then it can't pull no more than 13A. If the installation method permits adequate CCC and the CSA is adeqate for fault current/thermal constraints under fault conditions then technically there is nothing wrong with it.
True.....but he'll have to check....and that's gonna take time, man.:rolleyes:
 
True.....but he'll have to check....and that's gonna take time, man.:rolleyes:
I agree but we don't know what the OP was tasked with in the first place, If he were to remove the OCPD would that need a MNWC?
 
1.5 is the minimum for a power circuit, if the only thing connected is a fused spur then it can't pull no more than 13A. If the installation method permits adequate CCC and the CSA is adeqate for fault current/thermal constraints under fault conditions then technically there is nothing wrong with it.
What exactly were you there to do?
replacing like for like, just thought I'd do a quick Ze, IR and check the RCD and noticed the the 1.5 in the B32.
 
1.5 is the minimum for a power circuit, if the only thing connected is a fused spur then it can't pull no more than 13A. If the installation method permits adequate CCC and the CSA is adeqate for fault current/thermal constraints under fault conditions then technically there is nothing wrong with it.
That is all true but very close the knuckle.
VD works out at 2.02% so ok, is Ref method A (14amps) again ok but, the point of the FCU is to protect the cable from the FCU to the appliance and the MCB to protect the cable from the MCB to the FCU/accessory. In the event of eg. a line - neutral fault the 1.5mm would overload before the 32Amp MCB would trip.
 
Hager let through energy on a 32 amp mcb type B is 29kA so in this case the 1mm cpc for the 1.5mm twin and earth cable would be undersized and inadequate for fault protection.
I2t would be greater than the K2S2 of the cable.
Nope, that's going to take me much more research to figure out.
 
Nope, that's going to take me much more research to figure out.
For faults on current limiting devices such as bs en 60898 devices under 0.1 of a second then the I2t let through energy needs to be sought for compliance that the K2S2 energy withstand of the cable under fault conditions and thermal constraints is greater than the let through energy quoted by the manufacturer.
In the example of a hager mcb ,technical info I have then the 1.5mm is inadequate to be connected to a 32amp type b circuit breaker.
That is if the tripping time exceeds 0.1 of a second.
1.5 would be the minimum so the live conductor is satisfactory but the cpc being 1.0mm is not.
 
Hager let through energy on a 32 amp mcb type B is 29kA so in this case the 1mm cpc for the 1.5mm twin and earth cable would be undersized and inadequate for fault protection.
I2t would be greater than the K2S2 of the cable.

I'd like to see a domestic installation, after fault limiting by the DNO fuse, that has anywhere near 29kA I2t. I'd dare say you'd be hard pressed to find anywhere near 10kA
 
Hager let through energy on a 32 amp mcb type B is 29kA so in this case the 1mm cpc for the 1.5mm twin and earth cable would be undersized and inadequate for fault protection.
I2t would be greater than the K2S2 of the cable.

To get an energy let-through of 29kA^2 s on a Hager B32 you'd need a fault current of about 6kA, according to this graph:

Screen Shot 2018-01-26 at 12.34.35.png
(Source: Hager General Catalogue 2017) (p94 of the PDF)

For this particular device, 1mm cpc would be ok for fault currents up to about 3kA (max energy let-through 13225A^2 s (=k^2 = 115^2).

More generally, table B7 in the On-Site Guide gives minimum protective conductor size based on the energy limiting class 3 device (e.g. BS EN 60898/61009), this is the maximum energy let-through permitted by this standard. Individual manufacturers have a lower I^2 t than this, but the table gives a nice "worst case" limit.

As an aside, if you've ever wondered what the "3" in the square is, under (usually) 6000 or 10000 in a rectangle (which is Icn) on the side of a circuit breaker, then it denotes the energy limiting class of the device. I have never seen one that isn't a class 3. The alternative seems to be "class 1" for which there are no limits specified.

RCBO_markings.JPG
 

Reply to 1.5 mm T&E on a B32 MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
6K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock