Discuss 1 head, 2x properties- check meter in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
Afternoon

Looked at a rewire/ rear extension job today

They are turning the one property into 2- the ground floor side annex will consist of 1x dining/kitchen area and bedroom with en-suite (gas heated)
So electrical load will not be a issue

They do not want a new head and meter for the 2nd property becuase of the ££ of that

is there anything wrong with this:

head>> meter company meter>> henley block

henley>> DB1 of main house

henley also>> 100a check meter (consumers owns this meter now?)

100a check meter>> switched fuse isolator

switch fuse isolator>> DB.2 in side annex via a swa

100A Single Phase Digital Check Meter | ElectricalDirect - https://www.electricaldirect.co.uk/product/100a-single-phase-digital-check-meter-436268

or is there a better option?
 
I have seen a few properties in Bath with one cutout and 2 meters, one meter per flat.
Often see it in the large townhouses over 5 stories with a 3 phase cutout . basement and ground on one phase. first and second floors on phase 2, then 3rd and 4th floor on phase 3. each floor being an apartment with its own meter down by cutout and then swa going upto the consumer unit in the flat.
 
Sub meter?, in my world a check meter is a meter that is wired in series to the supply meter to check the meter accuracy of the supply meter. Otherwise it is a sub meter.
 
In the OP, the configuration means the main house will be billed for both the house and the annex as one property. The homeowner will then have to charge the family member using the annex through the check meter readings.
This check meter will not be calibrated as the DNO one is.

Call it what it is.... it’s a granny flat.
 
You can get sub meters that take a paper card.
The tennant purchases from the Landlord £10 or £20 cards and just inserts them into the meter as and when.
The landlord gets the bill for the main meter
 

Reply to 1 head, 2x properties- check meter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
I went along this morning to quote for an EVCP install. I thought it was a domestic house but it was a B@B. It has a 3 phase supply. I always...
Replies
49
Views
10K
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
Replies
11
Views
1K
Hi Have done some additions to an existing multibuilding non domestic site. I noticed no SPD on the mains intake side, they are in a reasonably...
Replies
13
Views
2K
Had a call out at a dental practice at 19:00 last night in the end I left the fault disconnect requiring further investigation. This fault not...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock