Discuss 1 switch, 2 fluorescent fittings in shed in the UK Electrical Forum area at ElectriciansForums.net

PHS

-
Reaction score
4
Just a quick one.
And I right in thinking I would take N/E from CU in shed to first fitting, take L from CU (with an E from fitting) all the way to switch, run switch L back to fitting and then just Dasiy L/N/E to next fitting?
not a lot of info on the web and didn't cover fluorescent fittings in the course.
Thanks in advance
 
Just a quick one.
And I right in thinking I would take N/E from CU in shed to first fitting, take L from CU (with an E from fitting) all the way to switch, run switch L back to fitting and then just Dasiy L/N/E to next fitting?
not a lot of info on the web and didn't cover fluorescent fittings in the course.
Thanks in advance
in this case then do what Murdoch has suggested and joint the neutral at the switch....
 
You have your part P in domestic installation .... not a question i would expect!!! If you are just confused as to where best to terminate the cables the its common to run T&E to fitting (L/N), T&E from fitting to switch (L/SW) and T&E from fitting to 2nd fitting (SW/N).

This utilises the fitting as the cable joint too...avoid running any wires passed the ballast inside.

They are various way to achieve the same goal but all depends on layout and installation methods....
 
Last edited:
I'm using singles.

So I got L/N/E from CU going to? Then onto ?
fittings both have a l/n/e terminal block in only
cheers
shoukd have just put a ceiling rose in lol

you can still use twin and earth for fluorescent fittings.

have you provided mechanical protection for the singles?
 
You have your part P in domestic installation .... not a question i would expect!!! If you are just confused as to where best to terminate the cables the its common to run T&E to fitting (L/N), T&E from fitting to switch (L/SW) and T&E from fitting to 2nd fitting (SW/N).

They are various way to achieve the same goal but all depends on layout and installation methods....

I do have part p yes, it only covered roses on the course and all the fittings I fitted on site were plugged into a click box. This is my first time fitting 2 fittings to one switch. Just want yo get it right first time cheers
 
I do have part p yes, it only covered roses on the course and all the fittings I fitted on site were plugged into a click box. This is my first time fitting 2 fittings to one switch. Just want yo get it right first time cheers

Their is no real difference whether a click or fitting ut sometimes you need to add an extra connector in the fitting for L-loop.... why not just wire 2 clicks and flex the fitting s then if thats more in your comfort zone.

My advice is circuit only, i assume as others are asking you have ensured correct earthing arrangements, bonding etc etc as part of the course of doing this work.
 
Well you need to have mechanical protection for cables throughout e.g. plastic conduit probably most suitable for you if you decide to stick with singles...
 

Reply to 1 switch, 2 fluorescent fittings in shed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
295
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
260
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
785
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock