Discuss 100A DP Isolator Installation Between Meter and CU in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

jaydub

-
Reaction score
24
Hi guys,

When installing a new CU does anyone ever install a 100A double pole isolator switch between the meter and the consumer unit?

Very often I come across 16mm tails which need to be upgraded to 25mm so I join the old tails to new in a Henley block and get the DNO to come and upgrade their side at their convenience.

Instead of using a henley block could I use an isolator instead?

In anyones opinion would there be any disadvantages to this?

I wouldhave thought having an isolator would be very handy but the meter guys hardly ever bother putting one in, even now.

They're also relatively inexpensive. Another thing, I cannot seem to finda 2-module metal enclosure so would this would be okay in a plastic enclosure? That to me seems like a bit of grey area.

Any help appreciated. Thanks
 
The meter installers will never put one in as this will increase cost.

And yes it does make sense to fit an isolator, especially as a lot of smart meters will detect when the fuse has been pulled and may not allow the power to come back on.

Plenty of switches out there to choose from: Wylex 100A DP Supply Isolator - https://www.tlc-direct.co.uk/Products/WYREC2S.html?source=adwords&ad_position=1o1&ad_id=45425533757&placement=&kw=&network=g&matchtype=&ad_type=pla&product_id=WYREC2S&product_partition_id=174057653827&test=finalurl_v2&gclid=CjwKCAiA-KzSBRAnEiwAkmQ157Kt_x523muqnFlf4y4TXEAW-EshYmwvjADqoV6nxokuHPGgm8Vz1hoCdV0QAvD_BwE
 
Murdoch, does it not specify in BS7671 that all supplies must now be 25mm regardless? Maybe I have misinterpreted this.
 
Generally the only time 25mm tails are a must In domestic are new builds where the local DNO requests 25mm tails and a 16mm earthing conductor as standard ,usually because a 100amp fuse has been fitted.
 
Metal or plastic. I've asked for my scheme technical a few times now as to whether such an isolator needs to comply with reg 421.1.201, and the response has been somewhat vague.

In fairness it would perhaps be more clear cut, where such an isolator would be installed in a domestic property. Not perhaps in an outside mounted meter box, but they would not give definitive answer. It would be down to 'the designer to risk access'. When the 18th draft was up for comment, I did suggest a better definition than 'similar switchgear'. Something to consider perhaps?
 
Metal or plastic. I've asked for my scheme technical a few times now as to whether such an isolator needs to comply with reg 421.1.201, and the response has been somewhat vague.

In fairness it would perhaps be more clear cut, where such an isolator would be installed in a domestic property. Not perhaps in an outside mounted meter box, but they would not give definitive answer. It would be down to 'the designer to risk access'. When the 18th draft was up for comment, I did suggest a better definition than 'similar switchgear'. Something to consider perhaps?

I've seen enough official guidance to convince me that a DP isolator does not fall under the wording or intent of that reg.
 
I haven't, can you share?

Similar switchgear assemblies
The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm
 
Surely you would only install one of those metal wylex switch fuse units when installing tails longer than 3m?
 
Similar switchgear assemblies
The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm

421.1.201 refers to consumer units and similar switchgear. In BS7671 Switchgear is defined as 'an assembly of main & auxiliary switching equipment for operation, regulation, protection or other control of an electrical installation'. That's sounds like an isolator to me?
 

Reply to 100A DP Isolator Installation Between Meter and CU in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock