Discuss 100ma 100amp 3phase main switch on TT system and rcd protection on the rest of the circuits question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
36
Hi all , my question for your brilliant minds is (ill first set the scene)

35mm 4 core swa coming from an external supply, 16mm earth ran out to an earth rod(ze at the distribution board main switch 0.35ohms)
now this is quite a large installation with a 3phase distribution board in the basement which also feeds a 3phase distribution board on the ground floor, and this installation is a large domestic new build house

now the question is: currently all lighting and sockets as well as any circuits that are installed in twin and earth/ hidden in ceilings etc are covered by 30ma rcbos , however the following are only covered by the 100ma rcd protection of the main switch (external air-conditioning / lift supply and pumping station)(all just standard c type mcbs)

am i right in thinking thinking this set up is ok ? or do i need to replace the non 30m rcbo fed circuits with 30ma rcbos

thank you for any responses in advance
 
All 30mA rcds will be necessary for additional protection to circuits that require it , such as cables concealed in walls generally less than 50mm from the surface which are NOT protected with mechanical protection or contained in earth metal containment such as conduit etc.
Circuits serving special locations such as bathrooms,
Socket outlets upto 20amp and for mobile equipment not exceeding 32 amps.
The lift circuit for example if installed in swa will generally not require additional protection and if a TT installation then the 100mA rcd will be for fault protection only tho not ideal as a main switch, tho will offer some discrimination to the 30mA rcbos if it’s a S type rcd.
 
sorry me bad the pumping station is 30ma protected as they needed 2 x socket outlets
lift is 16amp 3phase mcb ,swa fed radial
air con is 2 x 32amp mcb,3phase supply fed via swa
and 1 x single phase 3 core swa aircon radial
and also the sub main to the grd floor distribution is a 63amp 3 phase , fed with 25mm swa 4core with 16mm earth

think all C type(but would have to check the notes )
 

Reply to 100ma 100amp 3phase main switch on TT system and rcd protection on the rest of the circuits question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
849
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock