    As above, taking a Zs measurement on a circuit covered by a 10mA rcd. Tripping the rcd on a no trip, three lead test using a Megger 1721. Is there a change in the settings I’ve forgotten about to allow a Zs to be taken. Oh, testing at a socket rather than source.
    TIA
     
  2. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    No trip test tests at 15mA( or there abouts depending on the meter ) so it will trip a 10mA device
     
    • Agree Agree x 4
    • Like Like x 1
  3. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    Link out line and cpc at the end of the circuit and test using no trip setting at the device.
     
    • Agree Agree x 2
  4. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    If your going to the trouble of linking the line and cpc at the end of the circuit then you may as well measure the R1+R2 and add it to the Ze/zs/zdb or am I missing something ?
     
    • Agree Agree x 5
  5. polo1
    Offline

    polo1 Electrician's Arms

    Location:
    Glasgow
    Business Name:
    GW Electrical & Security
    For some reason I thought there was an option to reduce the test current on the Megger, but it appears there isn’t.
    So Ze +(R1+R2) it is.
    Thanks guys.
    PS can’t remember the last time I had to test with a 10mA rcd in place!
     
    • Like Like x 1
  6. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    If you have the line and cpc linked for R1+R2 then for the sake of a few extra seconds just test the Zs at the device instead of calculating.
     
  7. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Is that an approved test method?
    Never seen that method before, not in gn3 anyway.
     
  8. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    Not sure about GN3 but it is in the book "Practical Guide to Inspection, Testing and Certification of Electrical Installations" It was common practice before the introduction of no trip settings on meters.
     
    • Agree Agree x 2
    • Informative Informative x 1
  9. Loki
    Offline

    Loki Trainee Access

    Location:
    Devon
    I know you can change the mA, see 5:40 onwards. 10mA is the minimum setting.





    Edit: I've just looked through the megger manual & there's no mention of changing the trip current
     
    Last edited: May 14, 2019
  10. PEG
    Offline

    PEG Respected Member

    Location:
    Manchester
    Yep,you would need about 5mA ....not sure that would warrant a good enough test...i think rubbing me wooly jumper,produces more :)
     
  11. SparkySy
    Offline

    SparkySy Regular EF Member

    Location:
    Northamptonshire
    I tend to favour the link out and test at high current method, just because it's what I've done for years, and it gives me a more accurate measurement than the low current test most of the time, also it amazes me sometimes how much an rcd will influence the result if testing both way. BG rcds seem to be the worst for raising the Zs readings!
     
    • Like Like x 2
    • Agree Agree x 1
Loading...
Similar Threads - 10mA tripping test Forum Date
Domestic 10mA RCD for bathroom circuits Electrical Forum Saturday at 2:26 PM
Domestic RCD not tripping - tech advice Electrical Forum Friday at 10:06 PM

Share This Page

Users found this page by searching for:

  1. testing a 10mA rcd

Electricians Directory Post a Domestic Job Post a Commercial Job