  1. JakeF
    Offline

    JakeF New EF Member

    Location:
    Liverpool
    I know there’s the adiabatic equation to work earth size but generally if you install a twin and earth cable for distribution, do you need to worry about the smaller cpc size

    My situation is 20 metre 10mm t and e run and not using it to provide earth bonding. Will the 4mm cpc be adequate. 50A mcb not many circuits to feed.
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    what's the earthing arrangement?
     
  3. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Can you clarify what you mean by this? Earthing and bonding are completely different things, and "earth bonding" does not exist.
     
  4. JakeF
    Offline

    JakeF New EF Member

    Location:
    Liverpool
    Tncs
     
  5. JakeF
    Offline

    JakeF New EF Member

    Location:
    Liverpool
    Will the 4mm in the t and e suffice.

    Won’t be used for water and gas bond
     
  6. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    So it's just being used as a cpc then?

    Apply the adiabatic calculation to verify its adequacy then.
     
    • Optimistic Optimistic x 1
  7. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Show your calculations Jake.
     
  8. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    What's the Ze at source of circuit?

    Type/rating of OCPD etc?

    Installation method?
     
  9. davesparks
    Offline

    davesparks Forum Mentor

    Location:
    guildford
    Yes you do need to worry about it, whether it be a final or distribution circuit.
     
  10. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    The term ‘sub main’ suggests a distribution circuit.
     
  11. davesparks
    Offline

    davesparks Forum Mentor

    Location:
    guildford
    Yes I saw that, my point was that the same consideration needs to be given to both types of circuit.
     
  12. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    20metre run of 10mm T&E?
    is this an inside or outdoor run?
     
    • Optimistic Optimistic x 2
  13. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
    sub mains to and from would be help full .
     
    • Optimistic Optimistic x 2
Loading...
Similar Threads - 10mm submain Forum Date
10mm joined to 6mm for exterior charger Electrical Forum Nov 13, 2018
Domestic shower submain Electrical Forum Oct 15, 2018

Share This Page

Users found this page by searching for:

  1. submain cpc size

    ,
  2. what size fuse 10mm submain

    ,
  3. 10mm cpc

Electricians Directory Post a Domestic Job Post a Commercial Job