Last leg of domestic ltg circ,2 lt points seperately switched via 2g sw. At one lt point am getting 11v between neutral and sw live when sw is in off position No it fittings connected just connector blocks,any ideas what causes this,thanks
 
induced voltage due to proximity of conductors?
 
induced voltage due to proximity of conductors?
Yes agreed remember multimeters will pick up an induced voltage if you have a burglar alarm and set your meter to ac volts then measure across iether the DC + or- of the alarm panel to earth you will get the same affect because some of these cables run along side mains cable.
 
yes, if the earth is disconnected from the met and bonding pipes, you get a voltage in the earth wires, just like this. I dont think you should be too concerned
 
Try doing the same measurements with an analogue tester. Digital testers have a very high input resistance which makes them particularly sensitive to the induced voltages you're talking about.
 
Try doing the same measurements with an analogue tester. Digital testers have a very high input resistance which makes them particularly sensitive to the induced voltages you're talking about.
thats why i stll have my trusty AVO7
 
I also have a very old analogue which I won't part with. Digital testers are invaluable for some tests but can be very misleading for others. I've watched a few apprentices chasing faults that aren't there cause the digital tester shows a voltage....no offence intended 20al.
 
Agree, ...Digital testers pick up everything between the test prods and convert it into a reading on the screen, the sensing can be far too sensitive. Analogue multi testers however are slower and will generally read whats actually on the scale you have chosen. Which is why many of the better digital meters, will have an analogue bar-graphs that you are able to see ''trends'' as to what's happening in the circuit/component your testing.... When in doubt or getting confused readings with a digital meter, always have an analogue meter handy to confirm, or make clear what's actually happening.... lol!!!
 
Last edited by a moderator:
Had an analogue amp probe that measured resisitance and voltage as well and after 22 years I dropped in when we had the heavy snows and now I have digital
so ho hum
 
didnt know that about digital and analogue testers thats why this forum is the best i enjoy reading and learning from them keep up the good work bigglen
 

Reply to 11 volts at neutral in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
The other night, neighbour knocked my door. She said she'd gone to use their outdoor tap, and she thought she'd got a shock. Went and had a look...
Replies
17
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock