Hi all,
I'm new here but looking for some help with wiring a site transformer.

It has a 32A 3-phase supply. I can see the terminals where I wire the phases in to but I cannot see where I need to connect the neutral. The transofrmer will be dropping the voltage to 110V.

Where do I connect the neutral to? All help will very much appreciated.
If you ned any more information then please let me know.

Thanks in advance,
Mark
 
If the primary is delta wound it will not have a neutral connection so you need to check the primary configuration
 
Last edited:
I have got the transformer working - thanks UNG. Could anyone please explain how this works without a neutral from the 3-phase supply.

Many thanks.
 
NO Neutral required Having done 100s of site trannys put an earthclamp(bad practice I know) on your swa as when OINKS on site move tranys they dont care or notice that they have disturbed your gland and an earth clamp will at least keep the swa earthed Im assuming you are using 4core swa
 

Reply to 110V site transformer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
863
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock