The Opps manager of a regular repeat customer of mine has some issues with the 12v 50w down-lighters in his kitchen and bathroom

each light is supplied by it's own 12v 50w transformer, but the same 4 (out of 8) lamps in the kitchen and same 2 (out of 4) lamps in the bathroom keep blowing.

the replacement lamps were bought at different times by different shops, so it isn't a bad batch of lamps.
anyone have any ideas?
 
Are you sure its the lamps blowing (tested them) it could be a loose conection that makes again when they are moved when touched, over heating with insulation possibly. How long are they lasting ? are they going out together ?
 
Check the pins on the lamp. If one is pretty black the lamp holder is faulty.the lv lamp holder was the weak link in the system as they have roughly 4A running through them. U see to get lamp holders with screws which used to be much better.
 
get rid of dichroic lamps get to hot and waste of energy.replace lamp not fitting with 4.5watt led,suggest warm white.about £9.00 each.50000hrs 4 year gaurantee
 
Most gu10 led downlighters are directional ie they give a beam, not a spread of light i would go with warm white CFL lamps 7 to 13 w
 
LEDs;
I've tried "daylight" they are very efficient in Lumens/watt but they were just too "blue" in a white bathroom.
I tried "warmwhite" - they were too yellow for the bathroom, would look good in a living room.
I'm now on "neutral white" - they seem best.

Halogens;
"dichroic" lamps only reflect part of the spectrum downwards. They make the fitting run very hot indeed. I've replaced die-cast Al fittings which were completely distorted. Aluminium reflector Halogen lamp reflect the whole spectrum and make the fitting and the lamp run cooler and may stop the lamp giving up so frequently.

CFL;
Take time to warm up and produce sufficient light. Fine in a living room but you don't want to walk into the bathroom to have a **** and then have to wait for the lights to warm up :)

IP65 fittings are great, very safe, but they do let less of the light downwards and trap more of the heat.
Whatever you choose don't forget your fire hoods.

Laurie
 
Last edited by a moderator:
Recessed (ceiling) lights are classed as being outside of the zones altogether.

MY big worry is that the latest downlight fitting do not have a glass between the lamp and the room, and when you then fit an LED you have a gap between the lamp and the fitting. Not even IP4X.

I'm sure you are more experienced than I am so your thoughts on this are welcome.
Laurie
 
MY big worry is that the latest downlight fitting do not have a glass between the lamp and the room, and when you then fit an LED you have a gap between the lamp and the fitting. Not even IP4X.

I'm sure you are more experienced than I am so your thoughts on this are welcome.
Laurie

The original light had a IP4X light directly over the shower and the other three normal fittings. I felt that they were yo close to the shower so I upgraded all four fittings to IP4X fittings.
 
HALERS EVOLVLED 8w led sealed unit LED fittings 7 year warenty all IP rated ok they are a tad expensive BUT Well well worth it fit correctly walk away with no worries
 
BUy the LED driver (constant voltage transformer) as well as the lamps. Don't run them from the halogen transformer or the manufacturer won't stand behind you when you get the warranty call.

Laurie
 

Reply to 12v 50w downlights that keep blowing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello I have recently moved home and I looking to upgrade lighting across the house to LED. In the kitchen I have found that there is installed...
Replies
4
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi guys, Bare with me, hope this makes sense.... I have 3 separate mains (240v) lighting circuits in my kitchen all going back to a 3 way 1G wall...
Replies
4
Views
1K
I have just been in the process of changing some old 12v halogen downlights in the bathroom for bathroom for mains volt leds. My late father was...
Replies
2
Views
2K
Sorry for the long first post, I wanted to be as thorough as possible. On my landing I have a 2-way switch setup, one of which is 3-gang, one of...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock