Discuss 12v lamp above bath zone 1 in the UK Electrical Forum area at ElectriciansForums.net

kev

-
Reaction score
0
would this be acceptable
we have a shelf above the bath 1400mm high
wife would like a standard lamp on there
would putting a 12 led driver in the loft to supply the lamp be a ok
lamp would be secured to the shelf
 
It would depend on the IP rating for the luminaire, and does the manufacturer state its suitable for a bathroom?

Plus, bit unconventional :)
 
Yes as above, 25v ac or 60vR-F DC SELV or PELV, source outside the zones .IPX4 230v fixed permanantly connected luminaires permitted in zone 1 with RCD protection
 
Last edited by a moderator:

Reply to 12v lamp above bath zone 1 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
724
I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
I'm in Raleigh, North Carolina and have a well for my house's water supply. For some reason, pitless adapters, which allow all piping to be run...
Replies
1
Views
271
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
720
Hello, I am currently DIY upgrading a caravan with my girlfriend but need some advice. The (very old) 230VAC to 13.8VDC power supply broke down...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock