I'm currently in the middle of gutting the downstairs toilet. It will only have a toilet and a small cloak room sink.

I plan to have a mirror and x1 2 gang socket outlet for the misses to straighten her hair because she refuses to do in the bedroom because there is no mirror.

Is this deemed acceptable? It's not a bathroom or any other special location?

The consumer unit is on the wall behind the toilet so it makes sense to utilise one of the spare ways.

Quick thoughts on a circuit are to install a radial on a 20A mcb. 4mm t+e. Length will be amount 1 metre.

I would like a socket that's as flush as it can be against the tiles. I've seen this which looks good.

GU3220WPW - 2 Gang 13A Switched Double Socket in White Metal Flat Plate White Insert Schneider GU3220WPW - https://www.sparksdirect.co.uk/2-gang-13a-switched-double-socket-in-white-metal-flat-plate-white-insert-schneider-gu3220wpw#.WvWJPNAo9-E

Thanks
 
I'm currently in the middle of gutting the downstairs toilet. It will only have a toilet and a small cloak room sink.

I plan to have a mirror and x1 2 gang socket outlet for the misses to straighten her hair because she refuses to do in the bedroom because there is no mirror.

Is this deemed acceptable? It's not a bathroom or any other special location?

The consumer unit is on the wall behind the toilet so it makes sense to utilise one of the spare ways.

Quick thoughts on a circuit are to install a radial on a 20A mcb. 4mm t+e. Length will be amount 1 metre.

I would like a socket that's as flush as it can be against the tiles. I've seen this which looks good.

GU3220WPW - 2 Gang 13A Switched Double Socket in White Metal Flat Plate White Insert Schneider GU3220WPW - https://www.sparksdirect.co.uk/2-gang-13a-switched-double-socket-in-white-metal-flat-plate-white-insert-schneider-gu3220wpw#.WvWJPNAo9-E

Thanks
Why 4mm2 Gaz?
 
Because I have some in the garage ;-)

I probably should have said that really. Usually I'd wire 2.5mm on a 20a mcb but seems I have 4mm I'll use that.
OK Ta
 

Reply to 13A socket outley (downstairs toilet) in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock