W

Woodbeare1

Hi there can I describe an installation and I would love to hear some opinions as to weather the earthing is up to standard. Its quite a long run so I'm concerned about the difference between true earth and system earth!

Submain comes direct from meter cupboard in farmhouse through 100a main switch and 63a mcb

Sub main is 25mm2 swa 3 core using the 3rd core as cpc (also bonded to swa outer protection) it runs as follows

25m to adaptable box two CUs for cottage and workshop

Another 25m now goes on from the box to a 2nd shed with a AB and garage unit

From here it goes another 45m but reduces to 16mm2 swa 3 core to a barn with another AB and Garage unit

Here it reduces again to 10mm2 swa 3 core and goes through a 63a rotary isolator before running another 50m to the last shed.

I'm now about 150m from the meter cupboard and although the earth is sizeable I'm along way from the PME supply, should I be putting in earthing rods on a pme system??

Any help and constructive abuse greatly welcomed!!
 
Hmmm, quite bizarre. I was about to start a thread (hypothetical one!) on a similar tangent, but I'll let this one run in case the answer to my question comes up, and I save myself any unpleasant embarrassment. :)

To start the ball rolling for the OP, I would suggest the resistance of your protective bonding cable to any extraneous pipework might be high at the furthest point, or am I getting that completely wrong?
 
What type is the 63A mcb, what is the earthing system, what is the Ze, what size is the earthing conductor at the origin (to size bonding).
Is this a new years wind up.
 
is the farmhouse off the same supply? I think that further to exact calcs you will exceed max Zs that's only one aspect what is the aprox average load at each building as for volt drop.From what you have posted this distance is not in a staight line but each building has been added in turn.A better set up would of been out to each building from D.B. at farmhouse what would the longest run of been then ?.
 
Hi all sorry about the patchy details the 63a mcb is a B type and the cpc is 10mm2 and yes the farmhouse is on the same supply but the sub main comes off between the meter and the farmhouse CU
 
I'm assuming farmhouse is TNS or TNCS to its MET and DB1 is attached to that. And you are concerned about just how far away you can rely on the DNO earth (?).
One problem with the described daisy chaining of supplies between buildings has already been mentioned by AB in #6 - the cumulative voltage drop.
That led me to think about daisy chaining the bonding. I think the cable sizes described in reg 544 apply to each building and they are intended to link back to the installation MET (in farmhouse) individually from each building. Not daisy chained.
If that is correct, buildings after the farmhouse + 1 may need to be converted to TT (?). That may also address the increasing difference between the exported earth potential and the local. Just a thought :)
 
I assume main bonding is required in the cottage and the separate core of the 25mm cable, without other information should be adequate. Is bonding required in the other buildings.
 
I'm assuming farmhouse is TNS or TNCS to its MET and DB1 is attached to that. And you are concerned about just how far away you can rely on the DNO earth (?).

spot on Wilko am beginning to think converting everything after the workshop to TT might be the way to go!
 
I think that if you are happy with the loads not rising to give a volt drop issue and you do a TT after the point of the workshop the only problem to overcome would be the max Zs for the linked supply cable by what you have posted the existing buildings are daisy chained and there is not a practical way of supply other than the A.box at garage. what is your Zdb there ?
 
Pme should not be used in agricultural buildings unless a metalic earth grid system with multiple access points for testing is installed.
What type of buildings are these, metal framed.? If im reading your posts correctly that the 1st submain goes into a cottage then alsong as that zs figure is ok and all bonding in place i see no problem with that, i would then be thinking the first farm building should be tt with upfront s type rcd, then each building daisy chained off the buildings one to the next with suitable ocpd. Bonding each building frame work as you go along, aslong as 10mm cpc loops from one building to the next. If cpc/swa are smaller or only 2c is usedyou may need to individual tt each building.
 
is the farmhouse off the same supply? I think that further to exact calcs you will exceed max Zs that's only one aspect what is the aprox average load at each building as for volt drop.From what you have posted this distance is not in a staight line but each building has been added in turn.A better set up would of been out to each building from D.B. at farmhouse what would the longest run of been then ?.

Not sure ive ever encountered a set up where multiple outbuildings have individual supplies, usually theseare add on after add on!
 
So the 50Mtr run is being added from the garage therefore what is the Zs at this point can the 63A B mcb disconnect in time.
 
Hmmm, quite bizarre. I was about to start a thread (hypothetical one!) on a similar tangent, but I'll let this one run in case the answer to my question comes up, and I save myself any unpleasant embarrassment. :)

As this thread seems to have stalled, I will ask my question, and it may be pertinent in any case.

I was reading through the December issue of Professional Electrician, and there's a piece by Elecsa 'The earthing functions that can be performed by the armouring of a cable'.

On reading through it, I noted a passage that said in a PME installation 'the armouring (or a core) should not be used as a main protective bonding conductor', may have to carry sustained high currents which may result in heating of the bonding conductor.

It's a lift from GN8 (page 54) 'For installations forming part of a TN-C-S system in which the supply is earthed at multiple points (PME conditions applying), and it is intended to utilise the armouring of a cable or a core of an
armoured cable as a protective bonding conductor the designer needs to consider the effects of the currents that may flow in the conductor due to network conditions. The armouring or a core of such a cable is normally not used as
a protective equipotential bonding conductor where PME conditions apply unless the electrical installation designer determines that the heat produced in the armouring or core due to its use will not cause overheating of the live conductors of the cable when on full load'.

So my question (could be embarrassing) is how does the designer make that determination?
 

Reply to 150m submain to multiple outbuildings earthing (PME) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
784
I’m installing 20KW of Solar on my Barn roof, The barn is fed from a 3 phase supply originating at the house which is 80 meters away. I’ll be...
Replies
2
Views
1K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock