Take the tin hat off if you've got the fuse out de-rate the fuse to 60A there are millions of houses with 60A fuses that have had additional loads installed .

Precisely.

Got a client near me, 5 bed house, separate annex, loads of external lighting, pool, tennis court, ..... 60A fuse

People get so hung up about needing a 100A fuse ................... unless you are doing space heating, cooking and water heating and live in a big house you won't get anywhere near 100A.

Just imagine the lecky bill if you were running these loads on a regular basis.............
 
Ok - with k=115, S=16 and Ze 0.19 measured today, I get ... wait for it ...
Take the tin hat off if you've got the fuse out de-rate the fuse to 60A there are millions of houses with 60A fuses that have had additional loads installed .
Mine included ... that's why I'm pretty comfortable with 60A fuse :) .
Question is, do it myself (at least it's done) or ask DNO who may do it, or may not?
 
hmmm. tails inside the CU are basically in free air, but with a slight derating due to be in the enclosure, although with plenty of airspace around. IMHO methed C can be applied without losing any sleep over it. if i doubt, replace the cut-out fuse with 80A. 16mm only gets lukewarm @ 110A. BS7671 figures are more pessimistic than me giving up beer.
 
Using 230 x 0.95, I get 1,150A pssc and plugging that into 434.5.2, I get 2.56 seconds. The melting time for BS88-3 100A at 1050A is 0.4sec.

So for short circuit situation this 100A fuse will not damage the 16mm tails, if I've done that correctly :)
 
my old man's house, built 1926 has a 30A rewireable DNO fuse. it blew in 1988, but only when we;d added a 12kW cooker, 8kW shower,washing machine, and tumble dryer. all were going when the fuse let go.
 
Ok - with k=115, S=16 and Ze 0.19 measured today, I get ... wait for it ...

Mine included ... that's why I'm pretty comfortable with 60A fuse :) .
Question is, do it myself (at least it's done) or ask DNO who may do it, or may not?
K would be 143 as the earthing conductor is not incorporated as part of a cable
S= I2t square root /k
So I is 1210 amps
t I'd have to look up a bs 1361 or is it bs 88?
K is 143

Edit for some reason I'm working out the earthing conductor size so ignore me
 
Last edited:
I guess you must C2 every domestic installation that has 16mm tails and a 100 amp fuse arrangement without consideration other than 'it's not the right size'
This wasn't the argument, the argument was the rating of said cable and my proposition that being partially contained should reduce the ccc. You have yet to give a flaw to this argument.
 
This wasn't the argument, the argument was the rating of said cable and my proposition that being partially contained should reduce the ccc. You have yet to give a flaw to this argument.
You've yet to confirm yours.
Show me evidence that cables need derating and to what method?
Then I'll come around.
Don't recall bs 7671 requiring us to derate cables entering a consumer unit or an enclosure in the appendicies with the list of reference methods it gives.
 
Last edited:
As has already been stated if there was a requirement to de-rate a cable entering an enclosure for termination clipped direct and free air installation methods would not be possible and would not be in the BYB.
Clipped direct would apply between service heads and meters etc. Once contained at its termination to a CU alternative ccc applies. Really quite simple.
 
so what factor would apply to the cable rating just because it's inside a box? where in BS7671 does it say that a rating factor needs applying.
 
just for the craic, tne or other cables are usually stripped back to single insulated conductors inside an enclosure (so may closer reflect singles in trunking for that part), meter tails are usually sheathed right to the termination point. would this (how much?) affect the argument?
i've had a couple, there's no BYB in sight, i just wanted to get involved.. !
 

Reply to 16mm tails with 100A fuse ??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
789
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
974
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock