Not really sure what that question is about?
The maximum with an Ra of 2 ohms would be 25A, so all 3 of the answers shown, can be used.
Not aware of there being a limit of 100mA for TT installations.
Though I seem to recal something about 100mA max for fault protection and 300mA for fire protection?
However the question doesn’t mention fault or fire protection.