Had these on the 18 th exam,confused me a bit.
What’s the maximum Rcd that can be used ,when an Earth electrode Reading is 2 ohms.
100 ma
300 ma
30 ma.
What would you say is the answer.
 
with a fault current of 115A, what do you think will trip i 200mS or less?
 
300mA , but somewhere I recall BS7671 or a GN recommending 100mA for a TT installation ( presumably to allow for variations in the Ra)
 
Could they be relating to this table on page 64

20181124_081346.jpg


but from memory i thought you used a 100mA RCD on TT & then 30mA at board.
 
now that is interesting. the bit about insulated and sheathed cables meeting the requirements of double or reinforced insulation.
 
Yea,I actually ticked the 300 ma,being the max,obviously the ideal would be the 30ma.
nope. you'd have 30mA for final circuits. if you had a 30mA for fault protection, that would contravene the division of circuits and discrimination of RCDs in series.
 
at my age, i won't be taking the 18th, but if it was anything like 17th, i'd finished in 50 minutes, scored 87%, and that was at the age of 65. i could have done a bit better if i'd taken the time to look a couple of things up, but the pub was open.
 
at my age, i won't be taking the 18th, but if it was anything like 17th, i'd finished in 50 minutes, scored 87%, and that was at the age of 65. i could have done a bit better if i'd taken the time to look a couple of things up, but the pub was open.
Yea this will be the last I do,done 14,15,16,17 th,this was the most difficultist,its the new regs that disturb you.
 

Reply to 18th edition question in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock