I have been installing a 3 phase 60KvA generator connected to a MDU with a 100A 0.1A RCD, when I test the earth electrode resistance (Ra) using the earth fault loop impedance tester I get a reading of 1845 ohms, as this does not meet the Ra x Ia less than or equal to 50v, 1845 * 0.1 = 184.5 , it fails this test.
The ground seems quite dry and the earth electrode rod is under trees, I have tried moving the earth electrode, but still cannot get the Ra value less than 1845 - Have you got any suggestions as to how I can reduce the Ra ?