Discuss 2 Lighting circuits sharing same 6amp MCB in the Australia area at ElectriciansForums.net

O

olsonn

Looked at a job today and noticed 2 red line cables in one 6amp MCB which was marked up as Lights. The place is a small purpose built flat with a couple of lights in the entrance hall with stairs going up to the living area and the rest of the lights. The two way switch in the hall operates the hall lights in isolation and also the upstairs landing light. The landing light can also be operated by its own switch on the landing. Although the two lines shared the same MCB the Neutrals and CPCs were in seperate slots on the bars in the CU. I thought it would be a simple job to simply disconnect one of the circuits and put it on to the other RCD. This seems sensible given that the flat owner is in her 80s and lives alone and has to come down the stairs to reset the MCB when it trips in darkness. Well I connected one of the circuits to the other side of the board thinking this would solve the issue. I turned on the hall lights and they came on no problem. Ithen turned on the landing light from the downstairs switch and both RCDs tripped. I have put it back the way it was for now and it is working.

Does anybody know why it is doing this and how can I sort it out
 
Shared/borrowed neutral. You'll have to find where the neutral is connected, usually at the pendant at the top of the stairs, disconnect and make it safe, then run a neutral from the downstairs circuit to the pendant.
 
Might have had a new circuit installed to make a spare way or someone else found out about borrowed neutral and doubled up when the board was fitted and did not want the bother. tends to happen when no test is done before a board change by a £150 out in an hour sparks.
 
this was common practice in the 70's. the landing light has it's N from upstairs, but the L is fed from the hall switch. meant a 3 core between the 2 way switches wasn't needed. either keep the lights on 1 circuit, or run either a 3 core between switches or, if in tube, a single, then dis. the L feed from downstairs and feed as you would normally do from the landing fitting .
 
Not necessarily a borrowed neutral, it was quite common practice to run a ring for lighting in 1mm T+E in the 60’s to early 90’s.

To my mind it’s still a bloody good way of doing things but I always used 1.5mm. There again I wasn’t tied by the constraints of finance. They were my own houses or friends.
 

Reply to 2 Lighting circuits sharing same 6amp MCB in the Australia area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
538
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
550
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
360
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
764
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock