I have just installed a 2 phase system with 2 Solar Edge inverters (3.7kW per phase) Each pv system is fed through a shared Elster A1100 3 phase meter and each one runs fine on its own. When connected at the same time the RCDs on both system trip. The only way I can make it work is to bypass the generation meter, so the problem appears to be at the meter. We have done many single phase installations, and could use 2 single phase meters, but that requires two FIT applications, which seems mad!! Anyone got any ideas?
 
firstly, do you actually need RCD protection on the circuit under BS7671 17th?

if not, the solution to your problem is at hand.
 
And secondly, x2 single phase meters does not require x 2 applications. Although the computer might say no for the simplistic suppliers.

Have you got a diagram of how the rcds are connected? Perhaps a 3 phase rcd would do it.
 
Thanks for the replies.

It seems that it is an issue that the phases are being joined in the meter, which is enough to trip all the RCDs on both phases. The only way we seem to be able to get both PV systems working is by by-passing the generation meter (which somewhat defeats the object of having a Generation Meter!!).
Is there a multi-phase meter available that is electrically seperate inside, so it acts like two single phase meters but with a common display? Your thoughts are eagerly anticipated!
 
Not an expert here, but it sounds like you have joined 2 phases together, in the generation meter, so with one neutral you will be causing a huge imbalance, hence RCD problem.
Not too sure but could you use a 3 phase generation meter, but only use two of the phases? or just use 2 single phase generation meters.

One small point though, you have not balanced the phases by only have pV on two out of three.

Just some thoughts.
 
From my understanding of this, that could work, but two phases would still be connected at the generation meter.
Maybe it would be best is if the OP posted a sketch, or some pics, then we all would have a better idea.
 
+2 to Bruce's it's the obviuos solution
 
We've sorted it!! Thanks for the suggestions. We wired it up : inverter to RCD, then the 3 phase meter, then split out to AC Isolators on respective phases, then the seperate small Fuse Boards and on to the respective main fuse boards. Seems very obvious now, but just been used to putting isolators and meters in any order after inverter. Will know for next time!!
 

Reply to 2 Phase PV Problem with RCDs in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi I have three phase installed recently to increase generation. DNO approved the extra 2 solar arrays so we have 3.68KW FIT on one phase and 8KW...
Replies
1
Views
682
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
942
We have two single phase heat pumps on two phases of a three phase supply the third phase has an immersion heater. The heat pumps are set up as...
Replies
4
Views
1K
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock