question probably how would you test resistance of electrode on a tt system on a stand by generator.


firstly ask permission and notify the customer that the standby generator will be locked off thus premisses will be with out a back up power supply.
generator isolated lock it off and retain key
disconnect earth from generator
test equipment- earth electrode resistance tester
question may state length of existing electrode say 3m
so, current electrode must be put in 30 meters from the electrode under test and between the 2 is a potential electrode.
tester connections C1 and P1 connected to EUT c2 -current electrode p2 potential electrode
make a test at this point record reading
move potential electrode 3meters towards current electrode make a test and record reading
then move it 3 meters towards EUT from the initial point make test record reading
take the average of all 3 and each reading should be within 5% of the average if they are then the average of all 3 is the reading that is recorded.
disconnect test equipment re connect earth to generator

Read more: http://www.electriciansforums.net/i...ns/68577-2394-2395-exams-2.html#ixzz2OPF9LV92
 

Reply to 2395 electrode test standby generator answer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
565
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Dear All I have read several posts but still confused. I hope someone can shed some light on the Regs. 1. The Incoming Power Supply from the...
Replies
11
Views
6K
Hi there thanks in advance for the help iam still learning but soon to sit my trade test, on the booth picture number four is a TPN isolator I...
Replies
7
Views
1K
I live in the Philippines but I have the same US electrical system (2 x 110V hot + 1 x neutral). I have two ground rods buried 8 ft. deep and...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock