- Reaction score
- 5,940
Dan
Determine Earth Fault Loop Impedance (Zs = Ze + (R1 + R2) × Cr)
R1 = 0.387 (mΩ/m) From the On-Site Guide table I1,
R2 = From BS7671 table 54.7 Minimum protective conductor can be selected as the line conductor is 50mm² then the equation is S ∕ 2
∴ 50mm² ∕ 2 = 25mm² the next greater cable CSA is 35mm²
∴ R2 = 0.524(Ω/km) From the On-Site Guide table I1.
Ze = 0.08Ω, Cr = 1.28 From the On-Site Guide table I3.
∴ Zs = 0.08 + ((0.387 × 0.5) + (0.524 × 1) ∕ 1000) × 1.28 = 0.081
The maximum Earth Loop Fault Impedance for the Over Current Protective Device BS-88-2 160A is 0.27Ω From BS7671 table 41.4
so satisfactory
Determine line Fault Loop Impedance (Zn = Zne + (R1 + Rn)
Zne = Uo × Cmax ∕ Pscc ∴ Zne = 230 × 1.1 ∕ 5000 = 0.0506
Determine thermal compliance for short circuit
I²t ≤ K²S². From BS7671 table 43.1 K = 143, from the manufactures data t = 0.01
∴ 4962² × 0.01 = 246217 A²s ≤ 143² × 50² = 51122500
My question is this,
how should i end a cable calculation?
Do i need to work out short circuit thermal compliance or do i stop once i have ensured that the maximum fault current for the device has been confirmed not to exceed the rated?
Have i correctly work out my I²t or should i quote the manufactures data?
Regards
Dan
I have reduced your post in the quote to refer to some items on the calculations.
For the EFLI you have a given Zs as Zs = (Ze + (R1 + R2)) × Cr however you have not included Cmin.
The correction factor of 1.28 is for 90°C cables which also require that all terminations of those cables are suitable for that temperature, which is often not the case, so the limiting temperature would be 70°C in most cases and so a 1.20 correction factor. You have also used k as 187 elsewhere which is for 90°C as well. This may well be right but it is worth checking.
You have checked S/2 and got 25mm², so 25mm² cable would be OK, there is no need to go up a cable size unless the value exceeds 25mm².
I do not recognise Zn and Zne though they are identified by context but just seem odd in referring only to perhaps Neutral (n) and earth (ne).
You presumably have the PSCC (5000A) from your information.
A²s seems to jump in to the equation looking like a paste error.
Right now to the questions
I²t should be taken from manufactures data as the devices are current limiting and so the actual let through energy may be lower than a calculated value.
In practical terms if the fault current does not exceed the rating of the protective device then this is usually enough for installation calculations unless there is a reason to expect problems.
Check Volt drop, Zs, PSCC and if all is OK then installation can proceed.