    Hi,

    Been to a job with a 2core swa supplying the garage.. The swa has been glanded inside house to CU. But the other end in the Garage has had the swa run in plastic conduit with no gland on the swa so unable to test r1/r2.

    However the garage has its own earth rod. So technically the swa is earthed from the house end, with the garage having its own earth rod.

    The garage earthing TT is 37.0ohms, would I note this down as the garage r1/r2 circuit. Accepted with the 1667ohms as rcd?
     
  2. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Is this an EICR, or are you doing some alterations/additions in the garage. What is the house supply?
     
  3. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Do you mean R1+R2? r1 r2and rn are readings for RFCs (Ring Final Circuits)
     
    • Like Like x 1
  4. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Did you mean to quote the OP Pete :(
     
  5. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Not sure what you are getting at Middy, just trying to say to the OP that r1 and r2 are readings for r1 Live and r2 Earth as a single conductors, I thought he was meaning R1+R2 or am I getting tangled up somewhere?
     
  6. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Ohh okay
     
  7. jaydub
    Offline

    jaydub Regular EF Member

    Location:
    Suffolk
    Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?
     
  8. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    It's R1+R2
     
    • Agree Agree x 1
  9. jaydub
    Offline

    jaydub Regular EF Member

    Location:
    Suffolk
    I dont follow...
     
  10. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    You are trying to measure the loop of the L and E conductors correct? Which will give you a resistance reading noted as R1+R2 not r1+r2 a small thing but end to end reading r1 r2 and rn are recorded as RFC readings only, and are end to end readings of the L.N and cpc, get the basics wrong and other things will be wrong as well. Of course if you are insulating the armoring from the garage end why would you try and trying to measure the R1+R2 of the distribution cable.
     
    • Agree Agree x 4
    Last edited: May 31, 2017
  11. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    the swa earth is not part of the garge earth so R1/R2 is gonna be between L and the Rod E. If I read you right?
     
    • Agree Agree x 3
    • Disagree Disagree x 1
  12. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Hum.... Not sure what that would achieve.... Think about what you are testing
     
  13. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    My thought is the garage supply is a circuit off the main db (house CU) and this would have its own loop impedance from the SWA armour, which is its CPC. Then the sub board (garage CU) and the final circuits are the TT bit (?) .
     
    • Agree Agree x 2
    • Like Like x 1
  14. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    He is trying to verify earth continuity to the armour of the cable which is not accessible as it is contained within pvc conduit to isolate it from the TT, this earth continuity is applicable to the circuit from the house and nothing to do with the TT.
     
    • Agree Agree x 4
    • Like Like x 1
  15. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Perhaps we should just wait until the OP clarifies what he/she is doing?

    Edit; job wise
     
    • Winner Winner x 1
  16. jaydub
    Offline

    jaydub Regular EF Member

    Location:
    Suffolk
    Wilko has interpreted what I was getting at lol
     
  17. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    yeh but is it a circuit or just a piece of cable? Where is the loop hah!
     
    • Agree Agree x 1
    Last edited: May 31, 2017
  18. jaydub
    Offline

    jaydub Regular EF Member

    Location:
    Suffolk
    It would be a circuit wouldn't it, I guess it would be protected by an MCB in this scenario? I guess OP needs to clarify that
     
  19. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Well if it ain't a circuit how does current / fault current flow in it? Being creative, I'm thinking it's a >32A distribution circuit with a 5 or 1 sec disc time from 411.3.2.3 or .4 - at least it would be if I'd done it in 10mm :)
     
  20. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    The MCB in the house protects the cable. The circuit in the garage is separate imho.
     
    • Agree Agree x 1
  21. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    To the op I don't know the task you are undertaking but the EFLI or R1+R2 for the circuit from the house will be between the line conductor and armour of the cable which has been rendered inaccessible. This is the fault path for said circuit and has nothing to do with the TT arrangement. Whatever you are doing you will have to note the reading as Not Verified with the reasons.
     
    • Agree Agree x 3
    • Informative Informative x 1
  22. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    Spot on.

    Appoligise to everyone else for confusion.

    Pete, duly noted.

    The swa has been stripped back and the 2 cores run inside pvc conduit.

    I did a board change after the customer had an EICR report conducted. This wasn't highlighted and only became apparent when I begun testing after the new consumer unit was installed.
     
  23. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Wasn't confusing at all Robo.
     
    • Like Like x 1
  24. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    Thanks,

    I have put LIM in the box and noted on the EIC.

    They also pulled 2 strands from the other swa (another circuit) and connector blocked it and used as the cpc :/ no idea why they never glanded properly.
     
  25. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Exactly as Wilko said ,don't know regarding the position of the RCD however you will need loop reading /Ze +(R1+R2) to determine that the protective device for the sub-distribution circuit will operate within the maximum time for example if someone should accidently put a spade into the cable.
     
    • Agree Agree x 1
  26. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    The LINE (live) conductor SWA via the substation etc.
     
  27. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Will it have any reference to the choice of OCPD? cant see how as it's not being used as a cpc?
     
  28. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Ok so you verified a piece of cable.
     
    • Agree Agree x 1
  29. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Yes and I then can confirm it is safe to energise in the new consumer unit should there be a fault with the sub-distribution circuit the C.P. device will operate.
     
    • Agree Agree x 3
  30. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    However the OP was asking about R1/R2 vis a vis the garage assuming I read it right I am tired and somewhat sanguine tonight.
     
  31. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    I'm just into the 2nd glass :)
     
    • Like Like x 1
  32. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Jesus this is over complicated. He cannot verify continuity of the armour because it has been rendered inaccessible.
     
  33. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    The question seems to be about the garage unit
    Not the armour???
    I think I'll leave this subject for now night night.
     
  34. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    His initial problem was not being to access the armour of the supply cable to verify continuity and could he record the TT results for the supply cable, answer, no.
     
    • Like Like x 2
    • Agree Agree x 2
  35. driverman
    Offline

    driverman DIY

    Location:
    England
    Not that I'm into testing.....Could not the OP measure the TN Zs at incoming SWA cable at garage consumer-unit? Note reading and subject that reading from the Ze reading obtained at the house consumer unit giving R1-R2.
    Another way...use Method 2 wandering lead, assuming connection can be made onto the end of the SWA armouring using a probe.
     
  36. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    The final connection of the armour is not accessible.
     