Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss 3 phase 10kwp system in the Solar PV Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. bigsparks
    Offline

    bigsparks Active EF Member

    Hi All

    We are designing a G83 10kwp pv system to go on a 3 phase supply, using an SMA Tripower 10000TL. When calculating max AC amps will it be calculated at 10000 / 415v = 24/25 amps? We are looking to install one 4 pole AC isolator.

    Also what size tp mcb is is best to install.

    Thanks
     
  2. yellowvanman
    Offline

    yellowvanman Electrician's Arms

    Location:
    Dorset
    Thats not the way to calculate 3 phase currents. Assuming balanced

    Current = Power/3/voltage
    So in you case
    10000/3/230 = 14.5A

    Sanity check 3.68kW on 1 ph = 16A
    3 x 3.68kW = 11.04kw @ 16A /phase
     
  3. bigsparks
    Offline

    bigsparks Active EF Member

    Cheers for the reply

    So a 16a tp mcb will be suitable on this install then?

    UK Power Networks are the DNO here and up until recently they had been advising 3.84kw @ 240v =16amp was ok, which after speaking to them a week ago appear to have moved in line with other DNO's and dropped to 3.68kw per phase.
     
Loading...
Similar Threads - phase 10kwp system Forum Date
Commercial Replacing 3 phase circulating pump Central Heating Systems Wednesday at 11:30 PM
Has anyone seen 3 phase lighting Electrical Wiring, Theories and Regulations Wednesday at 7:50 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job