peterhardacher

Hi am currently employed as testing and inspection on a industrial site just wondered if you could give me some advise
What it is I got a 110 kw motor 180 amp 100 m run full load now I got a 75 mm cable supplying it . I have checked table 4d4a in the regs as it is 3 core armoured . Ref method E . According to this it says am allowed 207 amps without correction factors .

I have also done a cable calc 110000 w / ( 1.73 * 400v ) = 158 amp without power faction correction is this correct ?

I have been in Internet on cable calc program's for cable manufacturers which is telling me 75 mm

Now what it is the cable is protected by a HRC motor fuse 315m 355a according to Ib < In < Iz the fuse size is greater than the cable max amps

Also what concerns me is local to motor the 75 mm goes to a JB and reduces to 25mm I think because there is a lack of space for the bigger cable as the motor has other things around it . Now a 355 amp defo does not protect that cable in case of overload

Now one final thing this motor goes through a variable speed drive but even if it was set at 80 % I still have the problem of oversized fuse . Now I pointed this out to my boss he says its acceptable but I think he's wrong and as am signing the sheets I would great fully apreciate your professional advise on this thanks
 

Reply to 3 phase motor calcs cable sizes etc in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
542
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi all, I’ve been asked to run a cable for a 3 phase DC motor. Not having much experience with motors would you work out cable sizing the same...
Replies
11
Views
2K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock