    Hi I'm Darren and I work as a apprentice for a manufacturing company.

    I was testing a 3kw 3-phase motor as it blew a fuse and when doing my IR test down to earth I got a reading of around 11Gohms. I was under the impression that the reading had to be above 1Mohm which this is as far as I am aware but I was advised by my colleague that this is a bad reading and the motor is no good. Can someone confirm for me if I am right or wrong and why :)


    Thanks
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    that is an extremely high reading. as 1 Gig is 1000 Meg. most IR testers won't read that high. if it blew a fuse, i'd be inclined to IR measure between each winding and also a resistance test of each winding. if good, then fire it up with new fuse and measure currents.
     
    • Like Like x 1
  3. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    As tel said, you have you ohms mixed up somehow.

    Test all phases to ground again and between them @500v. Then check all the windings are balanced (the same).

    Does the motor run freely?
    Clamp on your ammeter and see what the FLC is.
     
    • Like Like x 1
  4. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    What the last two said, Tel and LeeH
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    or it could just be a tired fuse.
     
    • Like Like x 1
  6. Marvo
    Offline

    Marvo GMES....You absolute beauty. YOU ROCK DUDE!!!! Staff Member

    Location:
    South Africa
    I usually take a hammer to the blown fuse and post mortem it to see if it went with a proper bang or whether it was just a lazy blow.

    11Gohms is an enormously high IR reading, not sure why your colleague would be unhappy with it......
     
    • Like Like x 1
    • Agree Agree x 1
  7. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Cracking turn of phrase. I'll have to use it sometime.
     
    • Like Like x 3
  8. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    Yeah, lazy blows are no good. I like a little vigour.
     
    • Like Like x 2
  9. Marvo
    Offline

    Marvo GMES....You absolute beauty. YOU ROCK DUDE!!!! Staff Member

    Location:
    South Africa
    Yeah, some things lose (or gain) a little in translation :)
    Could have probably phrased that better.
     
    • Like Like x 1
  10. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    IR of a motor to blow jobs in 6 posts.

    Awesome.
     
    • Funny Funny x 1