This is probably a basic question but I have just wired in a large radial arm drill for a customer all working except the slurry lubrication pump. It has a 3 phase motor but only has 3 leads coming from the windings can someone explain how to go about testing this please.
I have done an IR test between each lead and the case all read >2000 the readings between each lead are >2000 >2000 & 600meg
There is no continuity between any of the windings using the ohms function of a multimeter.
Can I assume open circuit windings? What sort of readings would a good motor have.
There is 430 volts between each line and no current draw from any line.
Thanks