lurch
-
- Reaction score
- 43
Some advice please. . . I have a local community centre (old prefab) that has a 3 phase TNS supply from the local DNO. I have carried out a EICR which has unsatisfactory on various points, however I am trying to locate the regulation that covers isolation. . . . the scenario is 3 phases in to 3 phase meter, and then 3 separate single phase domestic Consumer units, all located within a cupboard.
My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.
My concern is that there is no single point of isolation on the 3 phase supply. I want to give this a C2 but not having come across this scenario before and want to know the regulation that covers this . . . if there is one. Or is it totally acceptable to have this setup as it is. . . . constructive answers always welcome.