Discuss 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
8
Hi I'm after some advice, ive been asked to connect up a new outbulding at a school, there was a building there before and the 4 core 16mm SWA was already in place. It will be a kind of extra classroom/club room and will have several sockets, lights and a small water heater in the toilet. Heating for the rest of the building isnt decided yet. I plan on fitting a 4 way 3 phase board and running everthing on seperate RCBOs. Probably 2 for lights, 2 for sockets, 1 for water heater and 1 for a fire alarm system. All circuits will obviously be 230v
My question is about the earthing. I thought about exporting the earth (main building TNCS) but im not sure the armour of the cable will be sufficiant. The main cable has also been joined including the armour. There are some main utilitys running under the building so if i TT it i know im going to drive the earth rod in to something! It also means putting a main RCD switch in and this will also mean ill have to try and find a double insulated gland to run the SWA into the board.
Any advice on this would be greatly appreciated.
 
Why do you think the armour is insufficient. Is it required to support main protective bonding.
 
Hi - with 16mm 4 core swa it's likely the armour will be sufficient for the CPC of the distribution circuit. But if there are any extraneous conductive parts in the 2nd building then it won't be big enough for protective bonding back to the installation MET in TNCS.
 
as previous. wtf do you want 3 phase over there ?
 
Tt is gland swa onto paxolin plate then bolt to base of dB and run earth straight from dB usaly 1 rod will get you around 30-40 ohms
You then have two different earthing systems in close proximity. The gland or end of The cable should be placed within an all insulated enclosure.
 
Tt is gland swa onto paxolin plate then bolt to base of dB and run earth straight from dB usaly 1 rod will get you around 30-40 ohms

That creates a dangerous situation because you have metal connected to two different earthing systems exposed inside the DB.

1 rod? How long, what material, what type of soil, whereabouts in the country, will that be ok for the available fault current?
 
We do lots of school work and I have yet to see a separate building with a single phase supply.
 
Do the adebiatic equation to see if the armour is sufficient for cpc, i would also consider using single phase only so you have the spare conductors to export the main earth at the main school.
 
It will be a kind of extra classroom/club room and will have several sockets, lights and a small water heater in the toilet. Heating for the rest of the building isnt decided yet.

We do lots of school work and I have yet to see a separate building with a single phase supply.

But 3 phase for the above seems OTT. What would you do? Put 1 phase for the sockets, 1 phase for the lights and 1 phase for the small water heater?
Or is the OP leaving spare phases for the 'heating, which isn't decided yet'?
I would be interested to know.
 

Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
645
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
671
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock