Is there an existing distribution board in the new building?
Discuss 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net
No its a new building, there was a mobile unit there a few years ago but there was just a cable left over. This building is meant to be more permenant. The cable was just disconnected in the main building DB. It runs under a playground so theres no chance of running a new one or thats the route i would have gone. I've been asked to reinstate the cable and fit a new DB plus a few sockets, lights and water heater for the toilet.Is there an existing distribution board in the new building?
Yep everything in the building will be new.Ok thanks so all new wiring then.
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.
There is no seperate CPC. The SWA is earthed but i wasnt confident in using this as a main earth for the installtion of the building because of the join.
Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net