Hi guys don't do alot of three phase so bare with me, am I right in thinking for example if your feeding three phase equipment say 60 amp, you size the cable on 20 amps per phase rather than 60 amp per phase, also where can I find info on neutral sizing in 3 phase systems, thanks
 
Hi Keith yes if it is 3 phase 20amps per phase then you size the cable as you would per phase.

In all honesty mate unless you are going to be working with some pretty hefty cables then basic rule of thumb is neutral the same size as phase.

It is quite an art to design a system where you have to be completely sure that if selecting a smaller neutral there is no chance of that installation every getting so out of balance that a smaller neutral is deemed acceptable. If you do go down the road of selecting a smaller size and the system starts to become out of balance then you can have real problems. I did once use smaller neutrals when designing motor circuits, where we were talking 95mm^ supplies and we used a 35mm^ neutral as all the loads were balanced and the neutrals were mainly for controls.

I do have some old college papers on this and If I can find them I'll post, but as I said for most designs unless your talking about very large cables I would design the neutral the same size as the phase.
 
Last edited:
Hi Keith yes if it is 3 phase 20amps per phase then you size the cable as you would per phase.

In all honesty mate unless you are going to be working with some pretty hefty cables then basic rule of thumb is neutral the same size as phase.

It is quite an art to design a system where you have to be completely sure that if selecting a smaller neutral there is no chance of that installation every getting so out of balance that a smaller neutral is deemed acceptable. If you do go down the round of selecting a smaller size and the system starts to become out of balance then you can have real problems.

I do have some old college papers on this and If I can find them I'll post, but as I said for most designs unless your talking about very large cables I would design the neutral the same size as the phase.


As above ^^^^ well explained without going in to it too far....

Also my gaffers name is Keith Sims... it's not you Keith??? His location isn't Sussex and is flaming useless on a computer so I assume I'm still safe!!!
 
Lol no it's not me, well it is me, but not the me your looking for!!

Your sounding like Lionel Richie now!!...... HELLLO

Just a confidence, allot of people put two m's in Sims..... We do it on purpose just to wind him up lolol

Anyway good to meet you other Keith
 

Reply to 3 phase in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
275
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
744
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
542
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock