Hi can somebody give me some help with this one, a yard for porta cabin storage and external 32A sockets fixed around the perimeter although the sockets are rated at 32A they have 16A mcb's fitted in the enclosure. leads are then run out to test the cabins and do maintenance,although the cabins have there own rcd protection should the trailing lead also be protected by an rcd at 30mA as vehicles drive around the site. there electrician kicked off when we were installing rcd's as he said he could not now test the cabins 5x trip.
many thanks.
 
411.3.3 Additional protection

In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:

(i) socket-outlets with a rated current not exceeding 20 A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32 A for use outdoors.

An exception to (i) is permitted for:

(a) socket-outlets for use under the supervision of skilled or instructed persons, or
(b) a specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.


Sticky one this, you cant really class a portacabin as "mobile" but as it's a socket outlet for use outdoors, there stands a possibility of other items being plugged in so I would be inclined to offer RCD protection.
 
thanks for your reply Lenny, that was my thinking,and the regulation i pointed them to, but need a bigger stick to hit them with.
 

Reply to 32A external socets and rcd protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock