I am installing final equipment in a new electrical installation and our equipment is fed via a local 3-phase 1:1 isolating transformer (Input is wired Delta and output is wired Star). Our equipment is all single phase and split across the 3 phases. It comprises many switch mode PSUs.
I have measured up to 50V between Neutral and Earth. This varies depending on load. This is obviously a concern, but since it is fed from an isolating transformer that is not referenced to earth, is this a problem?
We have questioned the main electrical contractor that is providing this supply, and they are now proposing to bond the Neutral star point on the secondary of the isolating transformer to the rebar in the floor. Currently the Neutral star point is NOT bonded to earth.
However I can't see why they don't just bond the Neutral to the supply Earth, on the isolating transformer secondary, to basically make it a TN-S supply. I didn't really understand their explanation for not doing this, but it was along the lines of preventing noise on the main earth / negating the isolation.
Can anyone else explain what I am missing here?
I have measured up to 50V between Neutral and Earth. This varies depending on load. This is obviously a concern, but since it is fed from an isolating transformer that is not referenced to earth, is this a problem?
We have questioned the main electrical contractor that is providing this supply, and they are now proposing to bond the Neutral star point on the secondary of the isolating transformer to the rebar in the floor. Currently the Neutral star point is NOT bonded to earth.
However I can't see why they don't just bond the Neutral to the supply Earth, on the isolating transformer secondary, to basically make it a TN-S supply. I didn't really understand their explanation for not doing this, but it was along the lines of preventing noise on the main earth / negating the isolation.