Discuss 3ph star delta starter motor drawing high amps in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
22
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.


Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
Is this a recent problem on an existing motor or an issue on a new install.
PS. No such thing as a star/delta motor.
 
could be a few things, im no expert on motorwindings but when they lose balance tends to be when things go pete tong, was there a reason it was stored away no longer used or was it working last time it was tested?
 
main-qimg-e11f98040c68f35a3d1cd631a1976404-c
 
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.
When you say the Starter runs OK with no Motor connected, are you saying the Starter operates as it should? and what do you mean by single speed?
If the Motor is starting, and connecting the Motor's winding in a Star configuration, but trips when it changes into a delta mode, then it sounds like you have either a faulty Motor, of you have it wired up incorrectly.

Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
Star delta starter / motor problem.
Starter starts runs as should on bench with no motor connected. Getting 230v to e on all 6 uvw 1s and uvw2. 415 u1 to v2 etc etc. But nothing 1 to 2s. As expected.
When motor connected up. (Single speed) it takes 3a in start on all . Drops into run fine but is taking 38a on all.
After 5 seconds it trips breaker.


Any ideas were to start. As both out of stores as spares and checking they work but now stumped
 
No not blown it out but it runs fine when connected to dol started with links in motor 3 wire.
It seems like losing a phase / low voltage high current???

Why do you need to start it via star delta if you are able to start it DOL, how big is the motor and are the windings rated 415/690 or there abouts?

How are you connecting the links when starting DOL I presume star as you say it starts fine when connected up to the star delta.

My bets on delta contactor in starter... although I can't understand from your original post if you've checked this?
 
Why do you need to start it via star delta if you are able to start it DOL, how big is the motor and are the windings rated 415/690 or there abouts?

How are you connecting the links when starting DOL I presume star as you say it starts fine when connected up to the star delta.

My bets on delta contactor in starter... although I can't understand from your original post if you've checked this?
https://www.quora.com/Why-is-star-delta-starter-preferred-with-an-induction-motor
 
Last edited:

Reply to 3ph star delta starter motor drawing high amps in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
Replies
19
Views
5K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock