looked at a rewire of a 4storey property today (lower,ground,1st,2nd)
they is a 100a 3ph head on lower floor- and there is 2x seperate SP c/u (think there use to be 2x flats)

but is now going to be one house

best option?... to install something like a 8way 3ph amd3 dis board by the head on lower floor and have all my circuits off rcbo's off that (balancing the load evening across the phases)

probaly do circuit wise:

lower floor lighting 6a 1.5
ground lighting 6a 1.5
1st+2nd floor lighting 6a 1.5
lower ground power 32a 4mm radial
ground power 32a 4mm radial
1st floor power 32a 4mm radial(with 2x 3m2 UHF kits)
2nd floor power 32a 4mm radial (with 1x 3m2 UHF kits)
kitchen ring 32a ring/radial
Indcution Hob 32a 6mm
Oven 20a 2.5mm
MW 20a 2.5mm
I.H 16a 2.5mm
Boiler 16a 2.5mm
Alarm 6a 1.5mm
Smokes 6a 1.5mm

no 'building' work is being undertaken as in extensions etc- so no building inspector- would I need a system grade A fire system as a large house or will I be fine will LD3 (smokes in 4x halls and heat in kitchen- all interlinked)
 
You'll struggle to balance 3Ph with all those 1Ph circuits.

Have you done your max demand calculation?

Could you get away with 100 amp 1Ph supply?
 
How come you are putting the smoke detectors on their own circuit?
It's it best to put them on a lighting circuit, then you will know if the RBCO has tripped?
 
You'll struggle to balance 3Ph with all those 1Ph circuits.

Have you done your max demand calculation?

Could you get away with 100 amp 1Ph supply?
as best as possible
split power radials, lights have a cooking appliance on each phase- should be even enough on a domestic enviroment no?
 
Just noticed, No showers?

As your client already has a 3 phase supply, I recommend keeping it, certainly for a 4 storey house, where future demand may increase.
They'll probably want a couple of meaty car charging points in 3-5 year's time.
 
Just noticed, No showers?

As your client already has a 3 phase supply, I recommend keeping it, certainly for a 4 storey house, where future demand may increase.
They'll probably want a couple of meaty car charging points in 3-5 year's time.
not electric showers no

i was thinking the high cost of needed rcbos, and not quite 100% even balance across phases outweights- possibly blowing the 100a single phase and having to add new single phase boards in at a later date
 
any advise on what fire grading is needed for a large 4storey house?
exisiting building just having a rewire- no structual alterations
You need a fire risk assessment to properly decide on what grade of FDAS you should install.
If the house is old and not being renovated then the risk may be greater and consequentially need a more robust system. If the house is of conventional high quality build then a grade D LD3 should be acceptable, unless the plan is to use the house for multiple occupancy.
 
with a property like that (over 2 stories)the people who mortgage/insure it and maybe even local council may insist on certain types of fire alarm, sound out the local fire brigade, they all have somebody driving round to offer advice and it is less aggro than the council and free aswell.
Having done quite a bit of work on multi storey town houses, most of them listed then we have had to ensure the cabling was all fire protected, fire blocks between floors, interconnected smokes/heats as a minimum and if more than 4 floors install emergency lights in the event of power failure, as if you are on 4th or 5th floor its a bit of a trek in the dark to get to basement to reset things. Always had another firm install the fancy fire alarm system when required as the firm I sub contracted for had lots of people on call.
Also you might want to check with the local building control as changing 2 flats back into 1 dwelling can come under a lot of different areas, regardless of what it is now, you are in effect creating a new dwelling as far as council are concerned. without the certificates from building control showing its up to standard and complies the property could be non-mortgageable and find insurance firms wont touch it.
 

Reply to 3phase dis inb domestic setup in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For a change its nice to have a clean slate to work to. Client wants their garage rewired (and boy does it need it!) so they can have the...
Replies
12
Views
3K
Hi Folks, I am in the process of building a log cabin in the garden and I am in need of some advice when it comes to the electricity supply. I...
Replies
9
Views
3K
Hi guys, I'd appreciate the opportunity to pick your brains a bit, and make sure I'm on the right track, please. (Will also be talking to my...
Replies
3
Views
2K
Hi everyone, Just purchased a new place and have already stripped out all the rooms as plan a complete renovation. Whilst everything is bare I...
Replies
45
Views
4K
So now what's the feeling these days on working out maximum demand for domestics, the OSG method has to go out of the window surely, with more and...
Replies
27
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock