Solarspark

Hi all .First post .

I'm an electrician working for a solar company company.

We have a commercial solar install starting tomorrow.

The array is split into three lots of 33kw . I can't be certain on very more details than that for the time being.

It will have 3 single phase inverters but be fed via a three phase supply. My boss wants to meter it at the switch room db. (origin of supply) . Then split the phases at the location of the inverters via a connection box and not use a DB.

Is it me or is he out of his tree ? I full intend to force him to consult the niceic over this. But I would very much like to confidently tell him that he is a numpty when I see him in the morning .

Shirley he either needs to install a DB at the inverter location or run three separate circuits from the origin of supply ?

What do you guys think ?
 
Out of his tree.

So this is a 100kW installation and he doesn't want protection on the circuits.....

Non compliant on too many fronts.

Or do you mean 3 x 3.3kW? You can create your own db from a single phase board with a 4 pole main switch and three mcbs one for each circuit. As you know, each circuit must be protected, so that it would be just as cost effective to buy a small 3 phase board.

Putting the meter in the switchroom is OK, however depending upon the distance, it may be better to meter nearer the inverter (get paid for the losses :) )

You say you are an electrician, just check BS7671 no need to consult the NICEIC...
 

Reply to 3phase supply to 3 single phase solar inverters in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi I have three phase installed recently to increase generation. DNO approved the extra 2 solar arrays so we have 3.68KW FIT on one phase and 8KW...
Replies
1
Views
682
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
671
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock