32A ring main, adding 2 more sockets off this, spark I’m working with says add radial 4mm to 2 new sockets from ring I’m saying extend ring? I know 4mm can take 32A but I wouldn’t do it his way
 
I agree with you, I don't think it is a very good idea. I expect it'll be fine and you'll never have any problems but you could say that about a lot of electrical work that is poor.

If this 'radial' extension of the ring circuit is at a point near the consumer unit or rather the beginning of the ring, then in theory the cable from the CU to this point could end up carrying more current than it's CCC and the 32A MCB may not trip. This is pretty unlikely but possible.

Also appendix 15 BS7671 does state that an unfused spur from a ring should only feed one single/double socket, although I am not sure how Industrial relates to BS7671.

lastly, I guess your friend is doing this because it is 'slightly' easier than extending the ring. In the future someone else may add to these sockets with more 4mm, due to the fact it is there and easy to spur from. Just because your initial work may not really be dangerous I think it's good to look ahead and think how your actions may affect future decisions.
 
Last edited:
Non-compliant and would show up on an EICR.

I am not sure how Industrial relates to BS7671.
Same as any other installation. BS7671 covers everything from a flat to a nuclear power plant.
 
A heater is also mentioned, which will probably be at least 10A. The likelihood is that the total load would be maybe 10-15A which could result in a long, slight overload to the 13A FCU that will not blow the fuse. Although technically compliant, I would say this is bad practice for an industrial unit just to save a bit of cable. At our workshop two doubles would often get loaded to 30A total.
 
How would 6mm² help?
 
Hi - my 20p : when starting with a change that's more than one outlet I would extend the ring circuit or make a new circuit.
 
I think the design issue with adding an unfused radial at a point on an RFC is it's got the possibility to have a 32A point load. The 2.5mm ring is ok for 32A OLCP based on the load being reasonably distributed around it, which won't now be the case.
 
Last edited:
Yes this ones been done to death, result is it's not a proper ring according to the informative appendix, but it can't cause an overload on the short leg as long as the joining point is more than iirc 15% of the way round the ring therefore it's ok in terms of minimise the chance of overload. Even with 2 double sockets near the end of a ring eg kitchen you could get overload so it's always a balance, just the 4mm spur stops the physical layout working in your favour.
 

Reply to 4mm spurred from ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
183
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
657
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
232

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock