  1. egginyourface
    Offline

    egginyourface Electrician's Arms

    evening all,

    I was told to run 2.5 cable from fuseboard to supply a 3.5 kw single oven. Job is done....

    Now they've said theyre going to put in a 5.3kw double oven in.

    Question i have is can I apply diversity to this and keep 2.5t+e or do i need to run a new 6mm,

    advice would really appreciated

    thanks
     
  2. a1guvner
    Offline

    a1guvner Electrician's Arms

    Location:
    Essex
    They want to change the spec, time for a variation order and some more dollar for you
     
  3. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    23 amps. Well technically 20amp fuse still exists so the cable is protected subject to normal de-rating considerations. Pushing it a bit IMHO. I think I`d recommend an upgrade in writing so if/when you have to go back to upgrade your covered. Sometimes these ovens have 5.3kw or something on them and that includes 3 elements say 2x grill and 1x rear circular fan element. As its unlikely or impossible perhaps to have the rear fan oven element on at same time as the grill you would be under 20 amps again
     
    Last edited: Feb 22, 2012
  4. TaffyDuck
    Offline

    TaffyDuck Electrician's Arms

    Cant say I can remember a job in a kitchen when it didnt change a bit so i usually bung 6mm in. These flippin electric range cookers are the nightmare at 10-11 kW.
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    as a1guvner says. alteration in design, extra work, extra cost.
     
  6. ample current
    Offline

    ample current Regular EF Member

    Location:
    Bristol area
    the diversity allowance for cooking appliances in a household is 10amps + 30% f.l ( full load if i remember right ) +5amps if the cooker outlet has an incorperated socket outlet.
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    which gives around 15A without a socket outlet ( top of head as calculator not to hand). so 2.5mm on 20A is adequate. problem would arise if they added a hob or changed to oven for a higher rated one.
     
  8. ample current
    Offline

    ample current Regular EF Member

    Location:
    Bristol area
    nearly telectrix 16.9 amps to be precise.
     
  9. egginyourface
    Offline

    egginyourface Electrician's Arms

    there is a hob but its on a seperate 6mm
     
  10. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    just worked it out. 5300/230 = 23A

    10A + (0.3 x 13 ) = 13.9A. where did 16.9 come from?
     
  11. egginyourface
    Offline

    egginyourface Electrician's Arms

    Can someone give me a step by step guide on how to calculate diversity as i havent used it for about 4 years...
     
  12. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    1.divide the watts by 230 to give a total load current figure.
    2. apply diversity: 10A + 30% of remainder = answer. add 5A if a socket outlet is incorporated.
     
  13. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    should add here that watch out for old BS3036s...as this affects the CCC of cables....as in for 2.5mm flat T&E on a BS EN 60898=27A....for BS3036=24A.........
     
  14. ample current
    Offline

    ample current Regular EF Member

    Location:
    Bristol area

    are you saying its 30% of whats left of the 23 amps after taking the 10 off? I thought the fl (in the osg) meant full load so 30% of 23 amps (not 13amps) ie 6.9 amps plus the 10
    equalling 16.9
     
    Last edited: Feb 22, 2012
  15. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    its the first 10A...then 30% of whats left......then if theres a BS1363 outlet incorperated into the double pole iso for the cooker....then just add 5A......
     
Loading...
Similar Threads - double oven fuse Forum Date
Diversity for a double oven Electrical Forum Nov 14, 2017
Name that brand! Double socket Electrical Forum Wednesday at 9:31 AM
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. what wire dose a 5kw built in double oven require

    ,
  2. cable size for 5.3 kw electric oven

    ,
  3. 20a fuse for 2.5mm.cable

    ,
  4. what size cable for a 5.3 kw oven,
  5. what amperage is a doible oven,
  6. 3.5kw καλωδιο,
  7. what amp require valfri doubld oven
Electricians Directory Post a Domestic Job Post a Commercial Job