Discuss 559.5.1 18th Ed. p219 Luminaire fixed connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

John-

-
Reaction score
48
Hi

559.5.1. My question is that for any luminare in the UK must be complaint to one of the methods (BS standards) listed in the list, or else we would not be compliment fitting and connecting to? Is that correct?

So if the fitting is not supplied with any details in relation to the points listed on p219, technically we cannot fit it unless we of course put something inside of it that does comply?

Thanks
John
 
559.5.1 Connection to the fixed wiring
At each fixed lighting point one of the following shall be used for the termination of the wiring system:
(i) A ceiling rose complying with BS 67
(ii) A luminaire supporting coupler (LSC) complying with BS 6972 or BS 7001
(iii) A batten lampholder or a pendant set complying with BS EN 60598
(iv) A luminaire complying with BS EN 60598
(v) A suitable socket-outlet complying with BS 1363-2, BS 546 or BS EN 60309-2
(vi) A plug-in lighting distribution unit complying with BS 5733
(vii) A connection unit complying with BS 1363-4
(viii) Appropriate terminals enclosed in a box complying with the relevant part of BS EN 60670 series or BS 4662
(ix) A device for connecting a luminaire (DCL) outlet complying with BS IEC 61995-1
(x) An installation coupler complying with BS EN 61535.
NOTE: In suspended ceilings one plug-in lighting distribution unit may be used for a number of luminaires.

Seems like just about everything is covered.
 

Reply to 559.5.1 18th Ed. p219 Luminaire fixed connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
505
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
I was away at the weekend & the electrician came round to fix something. While there he decided to condemn an outdoor electrical light as he said...
Replies
13
Views
2K
Working on an industrial radial lighting circuit, 6 son high bay fittings each connected from a conduit box via a short length of flex from the...
Replies
9
Views
2K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock