Hi guys some help required!! My sister runs a centre and has bought 5 x 3kw table top combined oven and hobs they are supplied with plugs which cant be removed as that will invalidate the warrentys. There are 3 spare slots on the consumer unit how can she safely run all 5 appliances. she says when in use the oven and hobs will be in use so will be running at full pelt. She had a spark in who suggested running 3 4mm circuits to serve the appliances. But just by browsing these forums and looking what you guys say I'm a little worried. Someone mentioned anything 3kw or above should have it's own circuit??
 
Hi guys some help required!! My sister runs a centre and has bought 5 x 3kw table top combined oven and hobs they are supplied with plugs which cant be removed as that will invalidate the warrentys. There are 3 spare slots on the consumer unit how can she safely run all 5 appliances. she says when in use the oven and hobs will be in use so will be running at full pelt. She had a spark in who suggested running 3 4mm circuits to serve the appliances. But just by browsing these forums and looking what you guys say I'm a little worried. Someone mentioned anything 3kw or above should have it's own circuit??

But this is what has been suggested no ? Separate circuit for each appliance ?
 
Hi - This is a big(ish) new load so it will also depend on the existing installation loads - hot water, central heating, existing cookers etc. So you definitely need @Murdoch to visit :) .
 
nothing to stop an electrician putting 2 of these appliances on a 32A or a 40A circuit run in 6.0mm cable. as they are fixed loads. overload protection is by the BS1362'sin the plug tops.diversity will also apply.
 
Hi guys some help required!! My sister runs a centre and has bought 5 x 3kw table top combined oven and hobs they are supplied with plugs which cant be removed as that will invalidate the warrentys.

Out of curiosity, what is the make/model, only very few manufactures state the above?
 
Well OP said 6 in his title and 5 in his question. Then when on to make things clear as mud. A picture or link would have helped. What do the manufacturers instructions say?
 
Well OP said 6 in his title and 5 in his question. Then when on to make things clear as mud. A picture or link would have helped. What do the manufacturers instructions say?

upload_2018-6-2_10-22-49.jpeg
 

Reply to 6 3kw table top ovens and hobs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
15
Views
550
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi we have a client who insists on using 3kw induction hobs on their projects. These hobs are used 8-10hours per day and come with a moulded plug...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock