Lc1

-
Reaction score
22
Good morning,
We have a load of approximately 18.5kw ( compressor skid). There is a plan to install a dedicated socket for this machine, the cable route is yet to be finalised and One of the contractors says 16mm2 cable 100A fuse is adequate but this comes from a rule of thumb as opposed to calculation. Is this a common rule for 63A sockets ?

Thanks
 
There isnt really a "common rule" it is entirely dependant upon cable length, installation method/route, size & type of protective device, ambient temps etc etc.

Get it designed properly then come back :)
 
without knowing the length of the run, i'd say 16mm cable on a 63A breaker is closer to the mark. i assume it's 3 phase. that equates to around 30A per phase.
 
You have to base the supply on the socket outlet because it could be used for any purpose.
 

Reply to 63A three phase socket in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock