Just been to a 1981 TN-C-S installation to fit new CU. Both Earth and Main protective bonding conductors are 6mm, which I understand was typical back then. 16mm tails with 60A DNO fuse.
Upgrading earth and bonding is gonna be tough as run up cavity and round the corner, I ain't never gonna pull a new cable through without some demolition.
There is no sign of over heating and all my Zs are well within tolerance.

Is there anyway of proving this is okay, or am I wasting my breath?
 
Just been to a 1981 TN-C-S installation to fit new CU. Both Earth and Main protective bonding conductors are 6mm, which I understand was typical back then. 16mm tails with 60A DNO fuse.




25mm tails
16 mm main earth terminal
10mm gas &water
..................................
16mm tails
10mm main earth terminal
10mm gas &water
.....................................
and so one or calculate it .
 
I'd upgrade the earthing conductor to 10 or 16mm and leave the bonding conductors as they are having proven continuity and a suitable method of connection.
 
The size of the main earthing conductor can be calculated using S=I2t square root/ K
Were I = the fault current
t= time for disconnection of protective device i.e. The cut out fuse in relation to the fault current
K= copper conductor either part or bunched with a cable (typically a value of 115) or separate (value of 143 for copper conductors max operating temperature of 70 degrees)

Bonding conductors can't be calculated in that respect and must be selected accordingly as per tables in chapter 5 in relation with the DNO supply neutral, not the CSA of the neutral that connects to the meter say.
If the bonding conductors show no signs of thermal damage and have been in place since they where installed with continuity then they maybe deemed adequate.
I would always try to upgrade but I appreciate it's not always that easy.
 
Last edited:
Check Reg 542.3.1 which supports Ian's view, but also refers us onto 544.1.1 for PME and onto Table 54.8 where 10mm is minimum.
 
The current best practice guides suggest a minimum of 6mm bonding conductors, if already installed and showing no signs of thermal damage, to be deemed as adequate and fulfilling the requirements of 132.16, regardless of earthing arrangement.
That'll do for me too.
 
Why would they show signs of thermal damage they probably haven't been put to the test yet, never say never I would change them to 10.0 if that proved to be the required size.
 
How do you know they haven't been put to the test as you say it?
Diverted neutral currents can still flow in the bonding conductors all be it rather low
 
This may be off interest to you?

The Electrical Safety First best practice guide no 1. Changing a Consumer Unit.

States that 6mm main earth and bonding conductors don't need to be changed when "they have been in place for a significant time and show no sign of thermal damage".

A pdf version is downloadable from their website.
 
Always happy to learn :)
My read is PME min earthing conductor is 10mm. Of course I may have misunderstood / misread BYB (?)
 
Older versions of bs7671 may not comply to today's standard but doesn't mean they are unsafe for continued use.

That is written near the front of the current edition of bs 7671

Exactly.
The requirements of BS7671 are applied to new installations. For alterations and additions to existing installations see 132.16 regarding earthing and bonding.
 
Older versions of bs7671 may not comply to today's standard but doesn't mean they are unsafe for continued use.

That is written near the front of the current edition of bs 7671
Not necessarily unsafe. In other words, non-compliances which at one time complied may or may not be unsafe and require proper consideration.
 
This may be off interest to you?

The Electrical Safety First best practice guide no 1. Changing a Consumer Unit.

States that 6mm main earth and bonding conductors don't need to be changed when "they have been in place for a significant time and show no sign of thermal damage".

A pdf version is downloadable from their website.
End of discussion, we have it it black and white from the idiots guide to electrical work.
 
End of discussion, we have it it black and white from the idiots guide to electrical work.

The particular idiots guide you mention is endorsed by the same organisations involved with writing the regulations that you said you would blindly follow regardless of new or existing installation.
Is the regs an idiots guide of higher calibre ?
 

Reply to 6mm Earth and Main protective bonding conductors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
677
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
745
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock