    6MM MAIN EARTH on a tt system with 100 ohm ze at db ,it runs under patio to rod .do i have to upgrade it as it means patio has to come up ? old wylex 6 way rewireable fuse board protected by old crabtree 60amp elcb i have to add a spur for a stannah stair lift and upgrade the non existing bonding customer not happy where do i stand?
     
    Last edited by a moderator: Feb 19, 2012
  2. R4BOE
    Offline

    R4BOE Guest

    is it mechanically protected ?
     
  3. Adam W
    Offline

    Adam W Electrician's Arms

    Location:
    Bournemouth
    Without checking the regs and to my recollection the minimum CSA to a rod on TT is something really small like 2.5mm, so 6mm is fine.

    ... After checking the OSG 2.5mm is fine if protected against corrosion and mechanical damage, otherwise 16mm if protected against corrosion and buried, or 25mm if unprotected.
    If not buried 2.5mm is ok if protected against corrosion and mechanical damage, otherwise 4mm, so again, 6mm is fine.
    Table 4.2

    So I suppose the question would be whether you would consider the main earth run under a patio to be 'buried'. Technically it is, but I can't imagine someone digging/drilling into it through the patio tiles.
     
    Last edited: Feb 19, 2012
  4. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk

    ..................
     
    Last edited: Feb 19, 2012
  5. malcolmsanford
    Offline

    malcolmsanford Trusted Advisor

    WP just for the sake of discussion, if that ELCB was current activated and you tested it, and if passed, would you still change it?
     
  6. IQ Electrical
    Offline

    IQ Electrical Trusted Advisor

    That's a good point, there was an ELCB and a VOELCB-the latter of which is now deemed not to comply.

    The main earth was usually taken to the VOELCB on a terminal labelled 'Frame' or 'F' whereas the ELCB will not usually have an earth terminal and will have an IΔn value on the front.
     
  7. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    Was taking ELCB to be a voltage operated trip....the old chilton one for example.....cant say I have come across any other sort apart from obviously RCD's.
     
  8. malcolmsanford
    Offline

    malcolmsanford Trusted Advisor

    [​IMG]

    WP here is a current operated one, I managed to track down on wiki................. I have to admit they would not be found in numbers like the old VOELCB you mean mate, as very soon after they were introduced, the actual RCD was introduced.
     
    • Like Like x 1
  9. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    Not come across one of those before malc......but I guess if it tripped within the required time it's ok to leave....??
     
  10. Engineer54
    Offline

    Engineer54 Guest

    Must admit, i can't say i've ever seen Matsu****a (Panasonic) protective devices used in the UK, especially at that time. Common as muck in the Middle and Far East.... and pretty decent too, apart from the protection curves offered, which are more akin to Yank curves!!!

    That must be one of the first DP RCBO produced ...lol!! Looks like it has a breaking capacity to match the re-wirable BS 3036 fuse boards it was probably installed with too!!

    Wonder what that ''Interchangeable type'' means ?? lol!!
     
  11. Adam W
    Offline

    Adam W Electrician's Arms

    Location:
    Bournemouth
    Judging by the black and white cables I would guess that that's not being used in the UK.
     
  12. tc50
    Offline

    tc50 Guest

    Thanks for your response man thats exactly what i done fitted rcd to that circuit only and bonded water and oil pipes which brought zs at d.b. Down to 60 ohms from 100 so worth doing.incidently i got a pfc of 4amps at d.b. Is this acceptable
     
  13. IQ Electrical
    Offline

    IQ Electrical Trusted Advisor

    I'm guessing you mean 4000A ie 4kA?
    Remember PFC is measured between L-E and L-N assuming a single phase supply.
     
  14. wirepuller
    Offline

    wirepuller Trusted Advisor

    Location:
    south uk
    You've measured PEFC not PFC.......
     
  15. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    For pefc 4 amps sounds alright.
    I calculate 3.8 from your results.
    Although the bonding will not reduce your Ze.
    Make sure you test the pssc as this will be higher in your case,
    And the highest result is recorded as your PFC.
     
Loading...
Similar Threads - main earth system Forum Date
TT off water main or tncs with no earth (Victorian house city centre) Electrical Forum Feb 28, 2018
Main bond to rubber incoming water pipe. Electrical Forum Friday at 2:58 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job