Hello All
Can any one provide non sarcastic suggestions as to why an 8.5kw shower has not tripped the 32amp mcb protecting that circuit?

Found this install in a domestic property. It seems to have been there for years, without out issue.

Thanks
DD
 
Im just dealing with something similar.
8.5kW on a 30A breaker. This one is actually tripping it, but only if the temperature is high and they spend too long in there.

As in the first post, have a look at appendix 3, page 370 of the new edition of BS7671 and you will see that it is highly unlikely a 32A breaker will trip with a 8.5kW shower (approx 37A-no calculator to hand).
 
Mines 8.5 KW shower is on a 30amp Cartridge fuse and been running spot on for 3 years since i moved in do have a spare Fuse sat in cupboard
 
If it's a B type it would need to get to about 46amps before it started to think about tripping.
8.5 kW @230v is about 37A.
See page 370. BBB

Remember a B type breaker only needs to disconnect within .4 seconds at 5 times it's rated current
 
A few years ago I upgraded a shower cable for a customer, it was an 8.5kW shower on a B32 breaker. It wasn’t tripping & had been in for over 4 years, however there was some discolouring on the mini trunking above the shower. The 2.5mm cable was working beyond its limits!
 
Like has been expressed, the trip curve characteristics explains why the 32amp doesn't trip but relative to design of the circuit we have a regulation that states small overloads for long periods should not be possible so anyone designing/altering this circuit should never have done that in the first place.
 

Reply to 8.5kw shower on a 32amp mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, hello, long time listner, first time caller... So, I have an issue in a house I'm trying to get ready to rent. The plumber has installed a...
Replies
17
Views
2K
I have 2 Mira dual valve vision showers. The remote control.for the Vision model has been discontinued, so I bought a Mira Platinum dual...
Replies
0
Views
174
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock