  1. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    Just arrived at a job, 45amp shower isolator completely burnt out.

    Checked cable and it's 4mm tne in trunking to 8.5kw triton riba shower on a 32amp mcb. Cable run is 5meters.

    This was a new circuit installed only a few months ago. I expect loose connection on isolator causing burnt terminals.

    I am going to request cable uprated to 6mm, anyone else make any sense why a 4mm was used?
     
  2. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    what type of switch was it? Pull cord or wall mount?

    FWIW 4 mm wasn't big enough to start with.
     
  3. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    That's all he had in the Van, or quite obviously he has miscalculated.
     
    Last edited: Aug 1, 2017
  4. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Or did he think at all - 4mm T&E was never going to be big enough IMHO
     
    • Agree Agree x 2
  5. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Ah sid it I'll stick some 4mm2 in, it'll be OK til it burns out, I'll be long gone by then, or something to that effect, or he's aDilbert.
     
  6. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    He put the 4.0mm on a 32 amp mcb,it was supplying a 7KW unit, its since been changed for the 8.5KW by the user:)

    Fantasy thinking I suppose but it often happens,think of 6.0mm and the purchases of the monster energy guzzlers by the ladies swooning over their size in B+Q
     
  7. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Deleted
     
  8. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Who in their right mind would run in a new dedicated shower circuit in 4mm?
     
    • Agree Agree x 1
    • Bad Spelling Bad Spelling x 1
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    someone who calculated that it was adequate for the load it served.
     
    • Funny Funny x 3
    • Agree Agree x 2
    • Like Like x 1
  10. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    Just spoke to landlord.

    Landlord purchased shower first and informed her other electrican what she had purchased, he then went and installed supply.
     
  11. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    This was condition of terminals when I arrived, MCB & RCD still in closed position.

    20170801_143409.jpg
     
  12. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    In which case landlord needs to get said spark back to replace switch and cable ......
     
    • Agree Agree x 1
    • Bad Spelling Bad Spelling x 1
  13. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    Shakes head!
     
    • Funny Funny x 1
  14. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Oh nice
     
  15. Rpa07
    Offline

    Rpa07 2000 posts - only 46379 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    And it's not the neutral this time!
     
    • Like Like x 2
  16. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I suspect the root cause of this was a loose connection and not conductor csa although it is obviously undersized.
     
    • Agree Agree x 4
  17. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    I've told llthe landlord to get other electrican to call me if he has any issues returning to sort, also when I undid the isolator Fascia the cables just fell out the back.

    I checked over the board before I disconnected the supply and some of the terminals were LOOSE :/
     
  18. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    but was not undersized for the 7kW shower, and was suitably protected with a 32A MCB. a bit like the chandelier i just repaired for a customer. 105VA transformer supplying 10 x 10w G4 lamps. he'd fitted 10 x 20w G4s and wondered why the transformer failed.
     
    • Like Like x 1
    • Agree Agree x 1
  19. robo83
    Offline

    robo83 Regular EF Member

    Location:
    London
    The landlord said they told the electrican what shower they were getting. And the sparks installed it with the cable, he must have known it was 8.5kw.
     
  20. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    even so, the 4mm would have handled that 8.5kW. it's down to poor terminations.
     
    • Agree Agree x 2
  21. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    ^^ even if I knew it was going to be a 7kw shower, I would still have fitted 6mm cable
     
    • Agree Agree x 4
  22. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Q+Q more like
     
  23. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    May depend upon the reference method used for installation as 4mm installed in trunking de rates to around 30 amps
     
  24. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    Sounds like he had plastic wrists
     
    • Funny Funny x 1
  25. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    I had a similar situation yesterday.
    Reports of shower isolator getting hot. Go to check it out. 6mm installed last year supplying a 9.5kw shower. Burnt out connections.
    I would always install a 10mm if wirring for a new shower.

    20170728_140007.jpg
     
  26. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Which is fine, and if you wish to do that then there is nothing preventing you from doing so. But if the calculations show that 4mm is suitable then you cannot criticise someone for installing 4mm, whatever your personal preference in the situation.
     
  27. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    10.0 doesn't prevent loose connections and burnt conductors.
     
    • Agree Agree x 8
    • Like Like x 1
  28. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    You're quite right.
    I always tighten connections. Leave them a minute to settle then u can normally get another quatre turn on them.
    The reason we always wire a new shower supply in 10mm, is so the customer has some flexibility when coming to choose a shower.
    And like ive seen before, when the customer decides on him/her self to uprate the shower to a 10.5kw. Not realising the existing 6mm will not be adequate. (Normally a trip back to b and q for them)
    I would always recommend not installing a electric shower, much better of a combi, but needs must sometimes
     
    • Like Like x 2
    • Agree Agree x 2
  29. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - not to disagree at all with ccc etc, but this pic does look like the heat is concentrated at the termination rather than evenly along the cable. And as the neutral seems unaffected (?) it perhaps suggests in this case the cause was poor termination of the line conductor?
     
  30. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    Hi wilko. Yes that was indeed the problem.
    Only been in for 8 months, so someone with plastic wrists must of installed it.
    I just think it's good practice to always install a 10mm cable for a new shower install.
     
    • Like Like x 1
  31. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    A job I'm starting a new build bungalow has been specified 16mm twin and earth for 10.5kw shower complete with a wall mounted isolation switch outside of the ensuite, which is a stud wall!
    Oh the joys.
     
    • Funny Funny x 1
  32. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    Good luck.

    Is that due to cable running through alot of insulation?
    Never seen a 16mm at a shower before.
    At least you can install a double 47mm metal box in the stud partition
     
    • Agree Agree x 1
  33. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Apparently 3 layers of insulation are going in so looking at reference method 101 even 16mm twin only pulls 46 amps reference method 101.
    At 10.5kw I'm looking at a loading of 43-44 amps so the 16mm will be able to handle it.
    I need to consult the builder and maybe request some boards are fixed above the insulation so a 10mm can be clipped above the insulation.
    They won't budge to a lower rated shower tho.
    Doubt I'd even manage to fit a 47mm box in the wall as the studs are only about 50mm deep
     
  34. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    That is a narrow stud
    Thankfully always 4x2 with the joiners we work with.
    Would not like to terminate a 10mm in anything less than a double 47mm box.
    To be honest don't like wirring showers fullstop :tearsofjoy::tearsofjoy:
     
    • Agree Agree x 1
  35. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    Don't like using them, but could u fit a 47mm faster fix box to give u that extra room.
     
  36. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I'll get round it as I really don't want to be installing 16mm but it's not mine or my company's spec
    4mm ring circuits as well.
     
    Last edited: Aug 2, 2017
  37. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I've used them on 10mm never on 16mm
    I can see the wall buckel as I try to push the switch back :eek:
     
    • Funny Funny x 2
    • Like Like x 1
  38. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    If it is already known that there will be that much insulation the. The electrical installation designer should first be trying to find a way to keep the cables out of it rather than plan for them to be buried in it.
     
    • Agree Agree x 9
    • Like Like x 1
  39. darkwood
    Offline

    darkwood For it is a human number, its number is 666 Staff Member Electrician's Arms

    Location:
    West Yorkshire
    If there is any kind of airing cupboard then a suggestion if re-routing the cable isn't an option would be a contactor operated by a lighting pull switch, cable size thus of no concern then. If the designer has issue with this then give then let them try terminate 2 x 16mm T&E into a standard shower switch and deep box.
     
    • Agree Agree x 5
  40. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    So true DW. First one I checked was Crabtree 50A and they won't accept bigger than 10mm2.

    IMG_0732.jpg
     
    • Useful Useful x 2
  41. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    The spec is deta accessories.
    So I'll have a look , think they only go as far as a 45 amp DP switch.
    Not sure on terminal size yet
     
  42. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    16mm for a bloody shower? bloody madness. these insulation freaks need to work round us and keep it away from cables. not vice versa.
     
    • Agree Agree x 3
    • Like Like x 1
  43. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Can only think running and terminating a 16mm2 T and E would be complete barsteward
     
    • Agree Agree x 2
  44. Des 56
    Offline

    Des 56 Trusted Advisor

    Location:
    Gliese 581C
    If I can manage to get my brain into gear,I think I will look for a logical regulation which frowns on such practices of using larger than life cable sizes on everyday accessories,extra naughty I believe :)
     
  45. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    slightlyoff topic, but hre's something that has been bugging me for ages.

    when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????

    thoughts???
     