- Reaction score
- 52
I was doing a eicr today. Came across a shower 9.5 kW Mira ,which had been installed for at least 8years.
its was brutally spurred off the bathroom heater which was protected by a 15'amp rewireable fuse. All, done in 2.5 t&e .
The client swore he knew nothing about it, and said he did have someone change the shower a good few years ago .
He also claimed it had never blown the fuse , I checked it was 15 amp wire , and I can only assume on cold days the heater was on as well and the shower was working hard.
Bizarre
To be fair the cable was still in good condition and belled out at 299.
whats going on here folks. It dosent add up!!
its was brutally spurred off the bathroom heater which was protected by a 15'amp rewireable fuse. All, done in 2.5 t&e .
The client swore he knew nothing about it, and said he did have someone change the shower a good few years ago .
He also claimed it had never blown the fuse , I checked it was 15 amp wire , and I can only assume on cold days the heater was on as well and the shower was working hard.
Bizarre
To be fair the cable was still in good condition and belled out at 299.
whats going on here folks. It dosent add up!!