It doesn't matter what ocpd you put as long as the cable has a low enough zs to trip it. If you have 0.01ohm ze and the cable is 3 feet long, you could put an 63a mcb on 1.5mm cable with a bell transformer at the other end.
The issue is the rated current of the shower being suitable for the cable.

Well there is a lot wrong with that statement!!

In that scenario the CPC will be destroyed in an earth fault.

Due to it being a transformer it has the potential to overload. The 63A MCB will never trip and the cable will set on fire.
 
I can't confirm that without more information.

Do the calcs, VD, PFC. What the Zs? What is the cable route, is it under a ton of insulation etc etc...

Did you not ask the other "Electrician" why? Or was it the same old story of "Just don't/Because it's something we always do"

Have you done any rough calculations? You aren't going to get a hard an fast answer off someone over the internet.
 
So will a 8.5 kw go on a 40A with 6mm cable an be within regs as another spark put the fear of god into me by saying DONT PUT A6mm ONA 40A
Do the calcs with all the correction factors and you will get the answer you need.
Then if you think the spark who put the "fear of God" into you questions it , show him your results.

The worst thing you can say to him is I went on a forum and they said.....
 
In that scenario the CPC will be destroyed in an earth fault
Good point, didn't think about adiabatic/let through from the low ze. Would need a happy medium. Would anyone calculate the cpc adiabatic for a 6mm shower cable?

Bell transformer i thought unlikely to carry an overload >20A+, that's tiny, just for the door bell push, but maybe more professional opinions vary. It would catch fire itself before burning the cable
 
Last edited:

Reply to 9.5kw shower 6mm cable in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
726
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
412
I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen...
Replies
19
Views
3K
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock