Can a 9.5Kw system be installed, commissioned and signed off without DNO notification and then notifying them or would gemserve or the supplier pick it up, if so whats the worst case scenario rather than waiting weeks?
 
If it is over 3 phases, then no problem.

If not, then don't do it. Worst case scenario? They find out about it and refuse your connection. And you'll have very little chance of getting a G59 install approved by them again.
 
G83 is for systems upto 16A per phase so a 9.5kWp system can be installed under G83 as long as you have used a 3 phase inverter or 3 seperate single phase inverters. So prior notification is not required.

Tom
 
the inverter need to be certified g83 compliant as well ! ( they would all pass its just a question of if your manufacturer did the paperwork as I understand it ) if not pm me we have in stock if you want to swap it out
 

Reply to 9.5kw without DNO in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
Hello everyone, I currently have two solar modules left over from an installation and I would like to use them to set up a solar system on the...
Replies
3
Views
880
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock