good afternoon guys
I have a 95mm 4 core swa to this new office build , thats fed via a new exterior mains panel located next to a new sub station.
now all feed cables on this project have been designed by an independent company, and i currently have flagged up that i believe that using just the steel armouring for both the cps and the bonding conductor is undersized.
details of the mains
300mm incoming cables from the substation
its a PME supply
95mm 4 core swa (200 amp) feeding one of the new buildings
new building has main water bond located within
now i have double checked that the smallest earth thats allowed should be 25mm, but when ive done my (very rough calls) ive come up with the steel adding up to 13.37mm
am i correct with the above
thanks guys